Stephen Prior wrote:

In older houses in the UK the neutral is bonded to a real ground at the fuse
box, where the ground is usually a long copper rod just a few feet away.

This configuration (TT) is rather rare (mainly rural supplies by overhead lines).

There is rarely in my experience more than a volt or two on the neutral.

More modern houses use PME (protective multiple earthing) where the neutral
is bonded not at the house but locally at the final step-down transformer-

The key factors about PME is that there is no earth wire from the sub-station, the premises earth being regenerated from the neutral at each property (TN-C-S). It also has neutral grounded to real earth at multiple points in the distribution network.

Whilst PME is increasingly used, "The Electrician's Gude to the 16th Edition of the IEEE Wiring Regulations BS 7671" (ISBN 0-9537885-0-4) suggests that the most common system is TN-S, where the the ground wire runs back to the substation and is physically grounded there.

the argument being that this forms a higher quality ground I believe.  The
real danger with PME is that the neutral may well then rise above 0 volts,

The danger is that mains earth, which is tied to neutral, can rise above true earth by a large amount (the example in the book is 96volts) if there is a break in the neutral between properties, as the return current then flows between ground rods.

but in normal circumstances, because plumbing inside the house is bonded to
'ground', no potential (!) exists for electrocution.  Until, that is, a ham
decides to ground his equipment 'properly' outside.  Then large amounts of
current can potentially flow!


--
David Woolley
"The Elecraft list is a forum for the discussion of topics related to Elecraft products and more general topics related ham radio"
List Guidelines <http://www.elecraft.com/elecraft_list_guidelines.htm>
_______________________________________________
Elecraft mailing list
Post to: [email protected]
You must be a subscriber to post to the list.
Subscriber Info (Addr. Change, sub, unsub etc.):
http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/subscribers.htm
Elecraft web page: http://www.elecraft.com

Reply via email to