Hi Jim,
 You wrote:

> The isolation aspect is limited to 60Hz
> isolation.  The prime power is
> ungrounded. It will be fed through the
> isolation transformer whose secondary
> will be grounded to form a green wire
> ground/neutral connection. For this I
> don't think I need interwinding screens.

You still have the problem if there is a primary feed/secondary 
short, where full mains voltage can appear on the secondary.  Low 
voltage secondaries my be sufficiently low impedance to take out your 
fuse, but high voltage secondaries(>120V) may simply get very hot 
while the external circuit suffers overvoltage.  The Earthed  interwinding 
screen effectively removes that possibility by providing a short 
circuit path to blow the supply fuse.
> 
> However, I don't quite understand your
> comment supporting switch on voltage
> peaks. This seems to me to be counter
> productive - or am I under a
> misconception. I thought I would need a
> switch on zero to minimize inrush
> current.

This is merely acknowledging that inductive circuits have 90 degrees 
lag on current.  If your transformer is unloaded on switch on, the 
current will be at a minimum when the voltage is at a peak.  These 
peak switching SSR's are produced just for that purpose, and are, in 
my experience, a God send.

Conventional resistive or loaded transformer switching can use Zero 
Cross Over switching, as the I and V are in phase.

Sorry about the confusion,


Chris Dupres
EMC Specialist. VG Microtech.
[email protected]
tel +44 (0) 1825 761077
fax +44 (0) 1825 768343
'Opinions expressed are personal, not necessarily Corporate'