Rich,

I like your analisys!  I agree completely.

You may recall that my initial opening statement was that there is no
intelligent answer (at this time?).

What I find really curious is the "official" 1 minute interpretation.  How are
we supposed to actually apply this?

I mean, UL/CSA fuses are calibrated down to 2 min (not 1).  So we can't approve
the circuit just by inspecting the fuse value; we must perform tests.

But these fuses will open after a MAXIMUM of 2 min.  There is no guarantee that
they won't open much faster.  In fact the very same fuse is allowed by the
standards to open after 5 (or 12) seconds, depending on the batch or the
manufacturer.  

What I'm getting at here is that we may perform a test using, by unfortunate
coincidence say, one particular fuse sample that just happens to be on the fast
side.  (A devious manufacturer may even be able to select such a fuse on
purpose, just for the safety tests -- nobody on this exalted forum, of course!
:-).  But the actual production samples will each have fuses that may vary
widely in opening time.  

So I can imagine a scenario where we will run the test and the fuse opens in 5
seconds and then everything is declared safe and hunky dory.  But the production
units have fuses that open in anything up to 2 minutes.  Seems to me that our
testing was completely meaningless!

Are we supposed to run the same test 2 dozen times (like when we certify a
fuse)?

So it appears that we can't approve the circuit just by inspection.  And we also
can't really get any reliable test results.

So how are we supposed to confirm compliance to this 1 minute limit?!

And never mind the 1 min limit itself.  I still contend that spraying molten
metal is going to happen in fractions of a second; not after 1 min.  I've melted
many screwdrivers during my TV and automobile repair days, and I assure you that
it all happens in a flash (please, don't ask me how long is a flash!)  And I
also suggest that any twit that is willing to stand there for a whole minute
while his finger is burning off, or while his face is getting sprayed with a
nice metallic conformal coating, deserves to be crippled!

:-)
Egon