I might be able to shed some light on some of it. 

The temperature rise is probably specified as being measured by the change in 
resistance method. The change of resistance method will average the internal 
temperatures and allows for a 5C hot spot. Hence, A 75 C rise, taken by the 
change of resistance method, equates to a hot spot temperature of 105 C. (75 
+25 ambient + 5 hot spot + 105). 
The same applies for the E and B classes. 
I can't account for the wider class F and H apparent discrepancies, I assume it 
goes along the same lines of reasoning.  

The above may be completely off base, since I do not have a copy of either 
standard, but may be helpfull. 

Gabriel Roy
Hughes Network Systems
MD
Of course the above are my opinions only, not corporate. 

-------------------- snip -----------------
Raymond Li wrote:


I have read through two international standards relative to the
captioned subject.  There are some differences even though they both are
called the same classes.

 EN 60 355-1   IEC 85

Class Temp rise   Actual temp
A 75 degC    105 degC
E 90 degC    120 degC
B 95 degC    130 degC
F 115 degC   155 degC
H 140 degC   180 degC

Since the readily available enamelled copper wires are largely quoted
American specifications as below, I am seeking some advice how to tie
the American approved/classified wires into European requirements.

 UL 506
Class Temp rise
105 70 degC
130 95 degC
155 115 degC
180 135 degC
200 150 degC
220 165 degC

Appreciating any expert advice.

Thanks and regards,

Raymond

 

Reply via email to