Richard,

As far as I know, about the only country that has a specific grounding and
bonding standard is Canada.  Check out CSA C22.2 No. 0.4-M1982.

BTW, all of the grounding methods you describe are acceptable:

1.  Dedicated post for just the safety earth wire lug.  Separate post for the
other bonding wire lugs.

2.  Only one post.  Safety earth wire lug/washer secured by one nut.  Each
bonding wire lug/washer secured by another nut.  Please note that it is also
acceptable to have several bonding wire lugs, secured by just one washer/nut
(one nut for the safety earth, one for all the bonds).

It is worth knowing that in the case of using a power cord (not your case),
where the power cord is wired straight into the equipment, several European
agencies want the safety earth wire to be on top of the stack.  Apparently they
consider a power cord to be likely to be replaced, so they want to disturb as
little as possible.

__________________________________________________________

 Egon H. Varju, P.Eng.  Tuesday, 17 September 1996 @ 7:59 PM
 Senior Engineer
 CSA Pacific Region

 Tel:   1-604-244-6640       HAVE MODEM  -  WILL TRAVEL
 Fax:   1-604-244-6600

 E-mail:        [email protected]
                [email protected]

 Disclaimer:  Opinions expressed above are strictly personal and don't 
 necessarily reflect the position of the Canadian Standards Association.
__________________________________________________________

Reply via email to