Ray & Others

I am helping several engineering groups resolve EMC & LV directive 
requirements here at Cutler-Hammer.  Some of the products are being 
evaluated/tested against EN61010 & UL3111 (equivalents).  Some of the 
existing products initially designed for the US market have MOV surge 
Suppressers on the front end.  Presently we have MOVs  Line to line and 
each line to ground.  These are wide ranging units rated 48 to 280 VAC for 
the power source.  Our applications are in power distribution gear where we 
are often very close to the source of the surge.  I have several 
comments/concerns/questions relative to your needs and for some of my own:

So far I haven't seen any obvious restrictions on using MOVs relative to 
EN61010/UL3111.  As per the CE mark and LVD I understood that harmonized 
standards have precedence over national standards.

All the same I have seen several examples of country safety standards that 
still have marketing importance.  For example I  understand that VDE and 
TUV have significant restrictions on the use of MOVs in power port 
connections.  How are others addressing this issue?

Nordic EN60950 - Although there is some parity between EN60950 and EN61010. 
 I have found EN60950 to be more restrictive overall. Are you not sure 
which standard your product will be required to meet ?  Couldn't you just 
stick with EN61010? 

Effectiveness of a line to line MOV when there is no grounded neutral -  
Ray I assume from your comments that you consider surge as primarily a 
common mode event.  In applying the IEC 1000-4-5 test there are both common 
mode and normal mode (asymmetric) exposures required.  Wouldn't the Line to 
line clamping still have value on the line to line asymmetric surges.

Application of MOVs -  One of my concerns with MOVs is the possible failure 
from too much power dissipation.  My experience is that the MOV can fuse to 
a short and then blow open, a messy condition. We have been careful to 
minimize this possibility however in case of this type of failure I have 
been researching what can be done.  Some ceramic PTC type fuses appear to 
limit the exposure however I understand they too can fail under surge and 
typically they are not rated for 230 V applications.  

Transient suppression without MOVs - What are the alternatives to MOVs?  I 
have considered and seen examples using inductors in each line.  What 
impedances values have engineers found effective to the 5 micro second 
surges (2-4KV ) of IEC 1000-4-5?  I have seen several applications with VDE 
565-2 recognized inductors  apparently designed for this application.  I am 
looking for sources that would be available in the US.  In addition to the 
inductors I assume that some additional filtering/clamping elements would 
be needed - any recomendations for an overall approach?

Ray As you can see I have some similar concerns. 
 I know I haven't answered your questions but by stirring the pot perhaps 
we can get some discussion going.
 
Chris Wells
Sr Des. Eng.
Cutler-Hammer
[email protected]

-------------
Original Text
From: C=US/A=INTERNET/DDA=ID/Ray(u)Russell(a)leco.com, on 5/13/97 6:42 PM:
     Dear Friends,
     
     It seems that surge suppressers have been a topic of much discussion 
     lately. Must be all of the surge testing to EN61000 4-5! Well at least 
     that's what brought up our issue. 
     
     We have a piece of 230V equipment that failed the surge test, (safety 
     testing will be to EN61010). In reviewing how to install varistors, we 
     have run into some concerns. In Europe the 230V supply is 1 line, 1 
     neutral, and 1 ground wire.  A  varistor connected between line and 
     neutral will suppress a surge, as long as the neutral is grounded. 
     
     For the 230V US voltage, there is 2 hot lines and a ground. To make 
     the varistor effective, it seems that the varistor needs to be 
     connected to ground.
     
     However, I know of a Nordic deviation out of EN60950 that states: 
     
     (DK, FI, NO, SE). Transient protection components shall be installed 
     in such a way that insulation for protection against electric shock 
     will not be bridged. This means that transient protection components 
     must not be connected to protective earthed parts in pluggable 
     equipment or to other accessible parts. 
     
     I think the concern here is the possibility of not having a good 
     ground, and then if the over voltage is shunted to ground, the chassis 
     could become hot. 
     
     Is this a valid concern? It sounds like a "double fault" scenario to 
     me. If so, does anyone have an alternative solution?
     
     Thank you for your consideration.
     
     Happy is the man that finds wisdom and gets understanding!
     
     
     Ray Russell
     
     [email protected]

Reply via email to