Heber and any with interest

Thanks for your feedback on the PTC /MOV application.  Help me understand.

My sense of the problem is one of power dissipation curves that must 
overlay properly.  The MOV has a joule rating that if exceeded will cause 
failure while the PTC  needs to dissipate enough energy  to engage yet not 
so quickly that the suppression of surge is not diminished.  Isn't it a 
relationship of surge energy < PTC trip energy < MOV joule rating, curves 
plotted with respect to time.  I imagine the real difficulty here is the 
long delay time of the PTC relative to the surge event and the MOV 
clamping.  I was hoping that with some limiting impedance in the PTC itself,
 one could balance the curves so that they are concentric (for lack of a 
better term).  That is the PTC could trip after clamping the surge and 
before allowing MOV damage.  

Am I close to understanding the challenge?

I mentioned on a posting that I had inherited a design where the engineer 
had attempted to make this relation ship work.  He had a Murata ceramic PTC 
(82 ohms impedance) in series  with the 120 hot and then a MOV in parallel. 
 As you said this combo does shut down the MOV but not until the MOV is 
damaged.  In this design the MOVs shorted but did not create a catastrophic 
failure.  I realize that preventing the MOV failure is a desirable goal.  

But isn't there some value in preventing the nasty flash over of a MOV 
failure?

Lastly - what do you know about the acceptance of MOVs in Europe and in 
that light how would you deal with Surge? 
 I have heard some contentions in particular when placed line to ground.  
What would you do:
1) Use robust front end filter and limiting impedances (resistors, caps and 
inductors) with no MOVs?
2) Put Gas tubes in series with MOVs.  (this sounds like a mess)
3) Fuse each MOV.  line to line and line to ground.  This way the fuses 
could prevent a short failure from becoming dangerous and then the fuse 
could be removed for specific applications that do not allow MOVs to 
ground.
4) Your new suggestion here?????
I am leaning towards #1 or # 3 but have no experience on selecting the 
right MOV/fuse combo.

Any feedback would be appreciated

Chris Wells
Sr Des Engineer
Cutler-Hammer
[email protected] 
-------------
Original Text
From: C=US/A=INTERNET/DDA=ID/hfarnswo(a)msmail.physio-control.com, on 
5/19/97 5:12 PM:
CWells wrote:
>>>I understand your concern in regards to the clearing time.  However the
PTCs are basically thermally driven and the so is the MOV failure.  I
believe one could balance the two with the proper sizing of the MOV and
the
series impedance of the PTC.

Wrong! A careful analysis will show that for any series combination of
MOV and PTC thermistor, there is a voltage just above the MOV threshold
where the MOV is still in a fairly high resistance mode while the
(unheated) thermistor is a low resistance. Since current is essentially
equal through the pair, heating will be largely confined to the MOV.
True, the thermistor will shut the circuit down, but not until the MOV
is damaged.

>>>I plan to talk to the various vendors of MOVs and PTCs.  If anyone has 
more
experience in this area I would appreciate your input.

Chris, I have extensive experience, including one patent (#5.379.022)
assigned to a previous employer. I'd love to hook up with someone
interested in a solution to this problem. Interested parties should
contact me by email ([email protected]) or at:
    Heber Farnsworth
    8029 137th Ave. SE
    Snohomish, WA 98290