Richard Huges wrote: >I am interested in obtaining data on the number, duration and amplitude of >mains transients at different parts of the mains distribution network. It >would be great if someone could point me to information published by the IEE, >IEEE or whoever. .......snip.........
>Information and constructive comments please. >Thanks (I hope!) >Richard Hughes Dear Richard Take a look at following articles: J.J.Goedbloed, Transients in Low-Voltage Supply Networks, IEEE Trans EMC., Vol. EMC-29, No.2, May 1987, pp.104-115 R.B. Standler, Transients on the Mains in a Residential Environment, IEEE Trans. EMC, Vol. EMC-31, No. 2, May 1989, pp. 170-176 F.D. Marzloff, The Propagation and Attenuation of Surge Voltages and Surge Currents in Low-Voltage AC Circuits, IEEE Trans. on Power Apparatus and System, Vol. PAS-102, May 1983, pp.1163-1170 They are all reprinted in "EMC/EMI Selected Readings", edited by V. Prasad Kodaly and M. Kanda (c) IEEE 1996, IEEE Order No. HL5734. In the the article of J.J. Goldbloed you will find a table of the amplitude distribution over 3400 hours, in Industrial, Business, Domestic and Loboratory environment. Abstract of table (transients over 3000V): Industrial - 28 Business - 61 Domestic - 0 Laboratory - 2 Hope it helps Best regards George -- ************************************************************** * Dr. Georg M. Dancau * HAUNI MASCHINENBAU AG * * [email protected] * EMC Lab * * TEL: +49 40 7250 2102 * Kampchaussee 8..32 * * FAX: +49 40 7250 3801 * 21027 Hamburg, Germany * ************************************************************** * home: Tel: +49 4122 99451 * Hauptstr. 60a * * Fax: +49 4122 99454 * 25492 Heist, Germany * **************************************************************