Richard Huges wrote:

>I am interested in obtaining data on the number, duration and amplitude
of
>mains transients at different parts of the mains distribution network.
It
>would be great if someone could point me to information published by
the IEE,
>IEEE or whoever.
.......snip.........

>Information and constructive comments please.

>Thanks (I hope!)

>Richard Hughes

Dear Richard

Take a look at following articles:

J.J.Goedbloed, Transients in Low-Voltage Supply Networks,
   IEEE Trans EMC., Vol. EMC-29, No.2, May 1987, pp.104-115
R.B. Standler, Transients on the Mains in a Residential Environment,
   IEEE Trans. EMC, Vol. EMC-31, No. 2, May 1989, pp. 170-176
F.D. Marzloff, The Propagation and Attenuation of Surge Voltages and
Surge
   Currents in Low-Voltage AC Circuits, IEEE Trans. on Power Apparatus
and System,
   Vol. PAS-102, May 1983, pp.1163-1170

They are all reprinted in
   "EMC/EMI Selected Readings", edited by V. Prasad Kodaly and M. Kanda
   (c) IEEE 1996, IEEE Order No. HL5734.

In the the article of J.J. Goldbloed you will find a table of
the amplitude distribution over 3400 hours, in Industrial, Business,
Domestic
and Loboratory environment.

Abstract of table (transients over 3000V):
Industrial  - 28
Business    - 61
Domestic    - 0
Laboratory  - 2

Hope it helps


Best regards


George


--
**************************************************************
* Dr. Georg M. Dancau             *  HAUNI MASCHINENBAU AG   *
* [email protected]             *  EMC Lab                 *
* TEL: +49 40 7250 2102           *  Kampchaussee 8..32      *
* FAX: +49 40 7250 3801           *  21027 Hamburg, Germany  *
**************************************************************
* home: Tel: +49 4122 99451       *  Hauptstr. 60a           *
*       Fax: +49 4122 99454       *  25492 Heist, Germany    *
**************************************************************