>The test setups I have seen for CE testing involve single phase
>equipments. Looking for thoughts on EFT tests of high current
>three-phase equipment.
>
>Do I need to run A-B, B-C, C-A, A-GND, B-GND, C-GND, ABC-GND,
>AB-GND, BC-GND, CA-GND?
>
>Are there other combinations which must be addressed?
>
>Who makes an EFT gen to handle 440 volts wye?
>
>jgs

James,

EFT testing is generally done to eacxh conductor with reference to the 
ground plane so you only need test each conductor (Neutral, Line phase 1, 
Line Phase 2, Line Phase 3, Ground) in turn.  Most test labs would run 
each phase (or ground or neutral) separately.

You would generally get a CDN (coupling-decoupling network) to connect 
between the EFT generator and the AC supply.  These are available from 
most of the generator manufacturers with price rising rapidly with the 
current rating of the CDN.  The CDN connects to the high voltage output 
from the generator.  Figure 4 in IEC1000-4-4 (or EN61000-4-4) shows the 
construction for the CDN.  You may be able to make your own if you have 
an old 3-phase LISN lying around. 


Mark

Mark Briggs
[email protected]

Reply via email to