Richard, 

I think that the standard is fine as it is with regards to fire enclosure. We 
chose materials within the enclosure which are self extinguishing so that we 
won't get a big fire inside the box. We also make sure that there are no 
openings in the bottom of the unit so that, in case of a fire,  flaming 
particles will not fall onto surfaces which may not be self extinguishing. I 
have seen capacitors catch on fire inside a computer but burn themselves out 
within a short time because of their being mounted on 94V-0 PCB, and in no case 
were any flames being shot out of the top of side of the enclosure. I think 
that you would have to have a pretty big fire inside a unit to have it do that. 

The standard never said that it would insist on enclosure being "flame-proof", 
and I for one don't think that this is necessary.  I can see making conduit 
boxes and fittings flame proof, but not necessarily appliances such as TVs, 
vacuum cleaners, VCR's telephones, radios, hair dryers, lamps, high-fi sets, 
etc. 

My opinion, of course. 

Gabriel Roy
Hughes network Systems
MD
(56)


------------------------- snip ----------------------------------------- 

Clause 4.4 of IEC950 (and clones) describes how to design ITE for
resistance to fire. The clause  is clear that the construction must
minimize the risk of spread of flame outside of the equipment.  Clause
4.4.5 describes what components require a fire enclosure, and clause
4.4.6 describes the construction of the fire enclosure. The latter
clause is very specific in the design of the bottom and sides of the
fire enclosure to prevent the spread of fire by dripping.  However, it
does not specify how to construct a fire enclosure to prevent the spread
of flames.  One might believe that clause 4.3.14 describes the
construction of the sides and top of a fire enclosure. However, a closer
review reveals that this clause describes the construction of openings
to prevent an electrical hazard and does not address the spread of
flames.

So, how is a fire enclosure to be designed to prevent the spread of
flame outside of the equipment? It appears that we must revert to a
subjective review of the construction in determining if an opening in
the side or top of a fire enclosure will allow the escape of flames. Of
course, the problem with a subjective review is that professionals can
and will disagree on the whether or not an appropriate solution has been
applied.

Does the standard need more work in this area? How do you determine the
size and location of openings in the side and top of the fire enclosure
to prevent the spread of flames? Your thoughts would be appreciated.

Richard Woods
Sensormatic Electronics

 

Reply via email to