Hi Eric:


I can answer one of your questions.

In Europe, the ELCB/RCCB/GFCI is an all-magnetic device and is
combined with the overcurrent circuit-breaker into a single unit.  
It is/they are located in the breaker box.  All outlets are
protected by the combined unit(s).  The main breaker and some 
dedicated high-current circuits use the "normal" circuit-breaker, 
i.e., without the ELCB/RCCB/GFCI function.

Because of the wiring and multiple outlets on the ELCB/RCCB/GFCI 
breaker, and because it is a magnetic (not electronic) unit, the
trip current is 20 mA.  The wiring and multiple outlets pre-load
the unit to maybe 10 mA or more.  So, the effective trip current
can be as low as 5 mA (the standard value for the North American
electronic units).

Europe does not have the ELCB/RCCB/GFCI built into the outlet as
is common in North America.


Best regards,
Rich



-------------------------------------------------------------
 Richard Nute                             Quality Department 
 Hewlett-Packard Company           Product Regulations Group 
 San Diego Division (SDD)          Tel   :      619 655 3329 
 16399 West Bernardo Drive         FAX   :      619 655 4979 
 San Diego, California 92127       e-mail:  [email protected] 
-------------------------------------------------------------

    ELCB  =  Earth Leakage Circuit Breaker
    RCCB  =  Residual Current Circuit Breaker
    GFCI  =  Ground Fault Circuit Interrupter