Hi Ron:


First, for assistance with an NEC issue, you SHOULD contact the
NEC authors, the NFPA.  They have the following web site:

    http://www.nfpa.org/

Click on:

    Proposals /
    Comments
    Query &
    Display  

Then click on:

    Staff Directory

Then click on:

    Engineering Advisory Service

Pick an expert that seems to match your questions, or click on:
 
    NFPA 70, National Electrical Code. 

This will enable you to send a message directly to NFPA.


>    1. Does the term (telecommunications network) refer to public or private 
>    networks?

Since the NEC refers you to UL 1459, then I would use the definition 
from UL 1459.  UL 1950 SHOULD use the same definition; see Sub-clause
1.2.14.7.  UL 1950 states:

    "A telecommunication network maybe publicly or privately owned."

>    2. Does the term refer to networks where overvoltage conditions can be 
> present? 
>    Maybe this can be assumed as UL1459 requires overvoltage compliance. 
> However, 
>    UL1950 provides for classifications of TNV circuits (Annex V).

For the purposes of UL (and therefore the NEC), telecommunications 
networks ARE subject to overvoltage (power cross) conditions.  See 
UL 1950, Sub-clause 6.6.  I believe UL 1459 and UL 1950 are the 
same in this respect.

>    3. Does the term refer to on-premise or off-premise?

UL 1950 does not contain any such distinction.  However, it does
provide examples of both public switched network and private networks
with electrical interface to the public network.  Since a public
network implies off-premises, I believe the term "network" includes
both on-premises and off-premises.

>    4. Will the 1999 NEC provide these definitions?

The NFPA web site includes all of the proposals for the next edition
of the NEC.  Click on:

    NEC
    Proposals
    and
    Comments
    Review  

Then, click on the box:

    Article 760 -
    Article 830
    (339k)

There are a number of proposals to change Article 800, including a
definition for "premises."  You can easily download these from the NFPA 
and check them out.  These are PDF files.

>    5. Is there any way for these questions to get to the appropriate NEC 
> committee 
>    for a response?

Yes.  See the NFPA web site mentioned above.  It does help if your
company is a member of the NFPA.


Best regards,
Rich



-------------------------------------------------------------
 Richard Nute                      Product Safety Engineer
 Hewlett-Packard Company           Product Regulations Group 
 All-In-One Division               Tel   :   +1 619 655 3329 
 16399 West Bernardo Drive         FAX   :   +1 619 655 4979 
 San Diego, California 92127       e-mail:  [email protected] 
-------------------------------------------------------------



---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to [email protected]
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to [email protected],
[email protected], [email protected], or
[email protected] (the list administrators).

Reply via email to