Hello Arjen:


The definitions for Class 2 and Class 3 circuits may be
found in the USA National Electrical Code, NFPA 70:

    Article 725-2          Definitions.
    Article 725-41(a)      Power sources for Class 2 and
                           Class 3 circuits.
    Figure 725.41          Class 2 and Class 3 circuits.
    Tables 11(a)           Class 2 and Class 3 Alternating-
                           current power source limitations.
    Tables 11(b)           Class 2 and Class 3 Direct-current 
                           power source limitations.

The index has an entry for:

    Energy-limited, Class 2 and Class 3 control and signal
    circuits [Article 725-41].

I cannot find any other mention of either Limited Energy
or Energy-Limited that apply to Class 2 and Class 3 circuits.

Article 725-41(a)(4) references UL 1950.  The specific
reference would be Sub-clause 2.11, Limited Power Sources.

I suspect this may answer your question as worded, but I 
suspect it does not answer what you want to know.  If you
will be more specific, I will try to answer your question.


Best wishes for the holiday season,
Rich





---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to [email protected]
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to [email protected],
[email protected], [email protected], or
[email protected] (the list administrators).

Reply via email to