Dear Mr Liew
Modern industrial products often use computer and switch-mode power
techniques which are a powerful source of RF interference, and to combat
this their manufacturers usually fit RF filters to their AC supplies.
Sometimes the filters are fitted to protect them from interference
carried by the AC supply.

The problem with these RF filters is that they generally have capacitors
fitted between their AC phases and earth, and this provides a leakage
path for current at the supply frequency (50 or 60 Hz). 

For example, at 50Hz a 4.7nF capacitor in an RF filter on 230 Vac will
leak 0.34mA, and a 100nF capacitor will leak 6.8mA. This is not a great
deal of current, but when you have a number of equipments all fitted
with RF filters and running from the same supply it can easily add up to
enough to trip an earth-leakage device. 

Also, when you have all these capacitors from phases to earth, a mains
voltage surge creates a similar surge in their earth leakage current.

People have been having similar problem with earth leakage in systems
comprising many items of equipment for many years! 

To prevent "nuisance" tripping of earth-leakage breakers The usual fix
is not to use an earth-leakage breaker at all! 

Or (more expensively) if you wish to preserve the safety features of the
earth leakage breaker - fit a 1:1 isolating transformer in the AC supply
between the earth leakage device and the offending equipment(s). The
transformer needs to be suitably rated for the load power, and should
also be over-rated to cope with the harmonic currents drawn by the load
(especially significant in variable-speed motor drive applications).
Power transformer manufacturers should be able to advise on rating for
load power and harmonics.

It is easy enough to find out in advance if a combination of equipments
will cause an earth leakage problem - just add up their earth leakages,
using either the figures specified by their manufacturers or measuring
them with an ammeter in series with their earh lead, and comparing the
total earth current with the rating of the earth leakage breaker. It is
not a good idea to allow the total earth leakage current to exceed 40%
of the breaker's trip setting or you will get a lot of "nuisance"
tripping.

You may also find it advantageous to use earth-leakage breakers that are
not very fast acting and will allow momentary transient currents to
occur.

Whichever route you take, the total earth leakages can be high enough to
cause a very real safety hazard for electricians who don't take care to
isolate equipment power before altering wiring. Since many RF filters
are fitted BEFORE the on/off switches in equipment they continue to
create earth leakage currents even when the equipment is switched off!
Consequently it is very important for electricians to always isolate all
the phases and neutrals of the AC supplies (i.e. switch them off at the
distribution switch-box) to the entire area of equipment they are
intending to work on. 

Since some filters may not be fitted with discharge resistors, it is
also a good idea to short all the phases, neutral, and earth together
(after switching the power off with a switch that isolates all the
phases and the neutral!) to discharge any charged-up filter capacitors. 

I hope this helps. All the very best!
Keith Armstrong
Partner, Cherry Clough Consultants


Liew, Shih Perng wrote:
> 
>      Hi All,
> 
>      I have some different machines in one production line sharing a same
>      power source, namely IX testers, ovens etc. I encountered a problem
>      where some of the ovens tripped-off intermittently. The earth-leakage
>      current was found to be excessive and causes the earth-leakage circuit
>      breaker to trip. To find a short-term solution, the affected ovens
>      were rewired from a new power source and the metal structures were
>      insulated. The problem seems to be solved...however, I am not so
>      convinced.
> 
>      Please advise if it is possible and how to find out before hand which
>      combination of machines will work together or could share a same
>      source without experiencing inteference. Can simulation method be
>      applide in this case?
> 
>      Bear with me if this doesn't make any sense, I am struggling to
>      understand the terms passed down to me at the moment.
> 
>      Thanks in advance.
> 
>      rgds,
>      sp

Reply via email to