Dear emc-pstc, A number of people responded to me, rather than the list so that 
I could consolidate the emails and pass them on to the list.  As most of the 
emails contained the same information and to conserve space and bandwidth, I 
picked several to pass on, which are included below.  If you would like me to 
pass on the others I will, just let me know.  

With all the information that was emailed to me, we were able to determine that 
following standards would probably apply to our product and the customers 
application:

   1. UL 913 (for intrinsically safe equipment).
   2. ANSI/UL1203 "Explosion-Proof and Dust-Ignition Proof Electrical Equipment 
for Use in Hazardous (Classified) Locations". 
   3. Article 500 of the National Electrical Code.

The product the customer was asking us about is a battery operated portable 
printer (To take a quick look at the product the customer ask about check the 
following web page :  www.monarch-marking.com/products/6035.htm.).  As Jacob Z. 
Schanker, P.E., said if you have to ask it probably isn't, and I agree with his 
comments on our product. Our product contains electrical and thermal energy 
sources, as well as DC motors with brushes, all of which could be problems under
the standards.   

I would like to thank the following people, who responded to my request for 
information: 

Robert Tims    [email protected]
Stewart; Judd       [email protected]
Jeff Whitmire  [email protected]
Constantin Bolintineanu [email protected]
Jerry Roberton [email protected]
Mark Briggs    [email protected]
Bill Burks / Rick Everett [email protected]
Roger Smith [email protected]
Gary Labadie   [email protected]
Eric Henning    [email protected]
Mike Morrow     [email protected]
Rick Cooper  [email protected]
Paul T. Kelly   [email protected]
Nick Ludlam [email protected]
Schanker; Jack  [email protected]
Kazimier Gawrzyjal      [email protected]
Jacob Z. Schanker, P.E. [email protected]
mike harris [email protected]


Jim
Jim Bacher,  Senior Engineer
Paxar - Monarch
email:[email protected]
voice:1-937-865-2020
fax:1-937-865-2048


------------------------------------------------------------
Author:  Eric Henning [email protected] 

Jim,
you'll probably get a flood of answers but check the National Electrical Code 
(NFPA 70) if you're in the US. article 500 describes hazardous areas but 
basically Class I, Div 1, Group D is:

Class I  (explosive gases)
Div 1 (always explosive mix available)
Group D (propane type gases)


other classiifcations are

Class II  (explosive dusts)
Div 2  (explosive mix only during abnormal or fault
conditions)
Group A (acetylene type gases0
Group B (hydrogen)
Group C (ethylene)
Groups E,F, G (dusts)

hope this helps.  typically Class I, Div 1 products need to be either 
explosionproof (contain an internal explosion) or intrinisically safe (not 
enough energy to cause a spark that can ignite a gas)  Typicallu you must go to 
an NRTL (UL, FM) to get an explosionproof approval.

eric
[email protected]


Author:  Mike Morrow <[email protected]>
This is a hazardous locations classification.  Class I = Gasses, Division 1 = 
gas present all the time, Group D = Type of Gasses (typically propane for Group 
D).  This comes out of the National Electric Code, Articles 500-505.  You will 
need an NRTL (Factory Mutual, UL, etc) certification in order to meet these 
requirements.  You can contact Bill Lawrence at Factory Mutual 781-255-4822 for 
further info.   They are a good place to start.

FYI, typical exams run in the 3-8 month range and cost 6-10K depending on the 
complexity of the product.

Mike Morrow
Product Standards Engineer
Data Instruments
[email protected]
[email protected]
Phone 978-264-9550 xt-201
Fax 978-263-0630



Author:  [email protected]

Mr. Bacher,

Since your customer referenced Class I, Division 1, Group D, I'll assume the 
application is in the U.S. or Canada. What your customer was asking you was 
whether your product was suitable for use in a hazardous (classified) 
atmosphere. In this case, an atmosphere of methane, natural gas, gasoline, or 
butane, just to name a few of the Group D gasses.  Petroleum plants and 
distribution facilities, as well as gas utility access areas are some examples 
where such equipment may be required.

If your product is portable or is part of a process control system, then UL 913 
(for intrinsically safe equipment) may be applicable.  If your product requires 
the use of an explosion-proof enclosure to make it suitable, then UL 1203 may be
applicable.  There are a few other possibilities and Canada has their equivalent
standards. Another source of information is Article 500 of the National 
Electrical Code which defines hazardous location classifications.

If you have any further questions, feel free to e-mail or telephone me.

Rick Cooper
Sr. Project Engineer
MET Laboratories, Inc.
410-354-3300
800-638-6057


Hello!

My name is Paul Kelly and I am in charge of UL's Hazardous Locations section 
here at our Northbrook, Illinois office.  Mike Windler forwarded your question 
to me regarding Class I, Division 1, Group D and I hope that the following 
proves helpful:

1. The marking string "Class I (Roman Numeral One), Division 1 (Arabic Numeral 
One), Group D" defines the characteristics of a "hazardous" (i.e. potentially 
explosive) area in accordance with the National Electrical Code (NEC).  See 
Articles 500 and 501 of 1996 NEC.

2. Class I indicates that the "hazard" is flammable gases, vapors or liquids.

3. Division 1 indicates that the "hazard" is likely to exist all of the time or 
some of the time.

4. Group D indicates that the ignition-related properties of the "hazard" are 
similar to propane.

5. Equipment installed in such areas must be protected by one of the following 
methods - explosionproof, intrinsic safety or purging/pressurization.

6. Explosionproof is a protection method that relies on the enclosure of an 
incendive arcing part to withstand the impact of an internal explosion and to 
prevent propagation of any flames from the inside to the outside of the 
enclosure.  The U.S. requirements for this protection method are contained in 
ANSI/UL1203, "Explosion-Proof and Dust-IgnitionProof Electrical Equipment for 
Use in Hazardous (Classified) Locations".

7. Intrinsic Safety is a protection method that does not rely on the enclosure, 
but instead relies on the "intrinsic design" of the circuitry to not be able to 
ignite the atmosphere under single or double fault conditions.  The U.S. 
requirements for this protection method are contained in ANSI/UL913, 
"Intrinsically Safe Apparatus and Associated Apparatus for Use in Class I, II, 
and III, Division 1, Hazardous (Classified) Locations".

8. Purging/Pressurization is a protection method that relies on the use of a 
"protective gas" to prevent entry of the hazardous atmosphere into the enclosure
of an incendive arcing part.  The U.S. requirements for this protection method 
are contained in ANSI/NFPA496, "Purged and Pressurized Enclosures for Electrical
Equipment".

        Note: Please realize that these "definitions" in Items 6, 7 and 8 above 
are only intended to convey 
        the basic concepts of each protection method.

9. Equipment utilizing any of the above protection methods can obtain a "rating"
of Class I, Division 1, Group D - but the certification evaluation would be 
distinctly different for each.

10. UL has an educational poster that details all of the above information - and
a good deal more.  If you would like complimentary copies of this poster, just 
let me know your address and how many you could use and I can have them mailed 
to you.

Let me know if I can provide any further assistance...

Paul T. Kelly
Associate Managing Engineer
Hazardous Locations
E-mail: [email protected]


The question was :
______________________________ Reply Separator _________________________________
Subject: What is Class 1, Div. 1 Group D?
Author:  [email protected] (BACHERJ) at Internet_Gateway
List-Post: [email protected]
Date:    6/9/ 0 8:14 AM


Yesterday we had a customer call asking if our products were Class 1, Div. 
1, Group D compliant.  Can anyone tell me where I can get information on 
what it is and what it takes to meet it?

Jim Bacher
Paxar-Monarch
[email protected]

Reply via email to