Jim,

Try National Electrical Code Article 500 Hazardous (Classified) Locations

Class 1 is locations where "flammable gases or vapors are or may be in the
air in quantities sufficient to produce explosive or ignitible mixtures"

Class 1 Div 1 is as above due to  1) normal conditions, or 2) frequently
because of repair operations/leakage/etc, or 3) breakdown/faulty operation

Group D is atmospheres such as acetone, ammonia, benzene, butane,
cyclopropane, ethanol, gasoline, hexane, methanol, methane, natural gas,
naptha, propane, etc

If your product carries a rating label with the above Class 1 Div 1 Group D
rating and a NRTL mark, you can claim to meet this performance level. If
not, I suggest to contact UL in Northbrook IL at 847-272-8800 to discuss
evaluating your product.

I used to work at Square D Co., which makes HazLoc electrical equipment,
and was responsible for building an in-house hydrogen-air testing facility,
plus testing with UL witnessing our tests for Listing.

My company helps manufacturers get UL and other agency certifications. If
we can help, feel free to contact me.

Mike Harris
Teccom Co.
[email protected]
707-258-1360/fax 1361

----------
> From: BACHERJ <[email protected]>
> To: [email protected]
> Subject: What is Class 1, Div. 1 Group D?
> Date: Tuesday, June 09, 1998 5:14 AM
> 
> Yesterday we had a customer call asking if our products were Class 1,
Div. 
> 1, Group D compliant.  Can anyone tell me where I can get information on 
> what it is and what it takes to meet it?
> 
> Jim Bacher
> Paxar-Monarch
> [email protected]

Reply via email to