Scott:

Here's a couple of comments and suggested possibilities to investigate in
tracking down the source of your problems.

1.  Check the turn-on time (not X-ray operation time) for the X-ray equipment.
The operator may turn on the unit, take one exposure, change film and set up
for a second exposure, take the second exposure and then shut down the unit.
That might account for the one minute (or so) duration.

2.  Check out any low-power, automatic, motor-driven vent controls in your air
conditioning system that may (only occasionally) come on during the day.
Noisy, brushed motors may be used for such operations.

3.  Don't rule out local sources generating power line conducted emissions
yet.  When the interference appears, quickly switch to a current probe and
sense the AC line cord noise/current.  Note the levels during and after the
interference.  Your AC line filter internal to the spectrum analyser may
preclude detection when you disconnect the signal input cable.  If suspicious
current differences are noted, resume your search internal to the company.

4.  Check to see if there are any pump controls nearby for storm drainage flow
control (or other flow control, such as irrigation).  These units are
periodically polled from a remote control site (or operate on timers), and
transmit a status to the remote site via RF links.  I have such a slave valve
site approximately 150 feet from my home and experience periodic bursts of
interference (for 60 to 70 seconds) on multilple TV channels.

Good luck,

Mike Conn
Owner/Principal Consultant
Mikon Consulting

Reply via email to