I too am re-posting an e-mail.  I'm pretty sure this one did make it
onto the forum, but I've only received one reply, so I am begging for
more, particularly to my questions 2 and 3 below.

Thanks,

Jim

> -----Original Message-----
> From: Jim Eichner [SMTP:[email protected]]
> Sent: Tuesday, May 18, 1999 11:21 AM
> To:   'EMC-PSTC - forum'
> Cc:   Tom Unger
> Subject:      RE: Surge Suppressors to ground
> 
> 
> Sorry to re-open a thread that is almost 2 years old, but here goes...
> 
> We are designing a product for 120V markets only, so there are no
> immunity requirements from a regulatory point of view.  We want to do
> what we can to ensure trouble-free operation though, so we are looking
> at up to 3 MOV's on the AC input:  one line-to-line and one from each
> line to ground.  The line-to-ground MOV's have been the subject of
> much
> discussion regarding various European agencies disallowing them, and
> we
> don't really want to give up the real estate that they would take up,
> anyway.  On the other hand, common-mode transients are a real world
> event, so we're having trouble making up our minds.
> 
> My questions:
> 
> 1. Am I correct that the North American agencies (CSA, UL, ETL, etc.)
> allow line-to-ground MOV's?  The standards we work with do not
> disallow
> them, but this is the sort of issue for which agencies often invoke
> "desk drawer requirements".
> 
> 2. Many of you have lots of experience with surge testing for European
> compliance.  How common is it (relative to differential mode surges)
> for
> common-mode surges to cause upset or damage?  Just as common but it
> takes higher voltages / currents?  Less common even at higher levels?
> 
> 3. Does anyone have any real experiences with the supposed shock
> hazard
> that has caused several European agencies to ban line-to-ground MOV's?
> 
> Thanks for your help,
> 
> Regards,
> 
> Jim Eichner
> > Senior Regulatory Compliance Engineer
> Statpower Technologies Corporation
> [email protected]
> http://www.statpower.com
> Any opinions expressed are those of my invisible friend, who really
> exists.  Honest.
> 
> > -----Original Message-----
> > From:       richn@anetMHS (Rich Nute){MHS:[email protected]} 
> > Sent:       Wednesday, May 14, 1997 3:36 PM
> > To: WOODS@anetMHS (WOODS RICHARD){MHS:[email protected]};
> > JEichner; bceresne
> > Cc: emc-pstc@anetMHS (Product Safety Technical
> > Committee){MHS:[email protected]
> > Subject:    Re: Surge Suppressors
> > 
> > Hi Richard:
> > 
> > You commented that the major reason a surge suppressor
> > is not allowed from line to earth is because the surge
> > suppressor is prone to shorting.
> > 
> > Let us assume that the surge suppressor only fails when
> > a voltage is impressed across it.  
> > 
> > For a voltage to appear across the surge suppressor, the 
> > chassis of the product must be connected to ground.  If 
> > it is not connected to ground, then there is no current, 
> > and there is no voltage across the suppressor.
> > 
> > So, a surge suppressor can only fail when the product is
> > truly grounded.  If it is grounded, then the grounding
> > SHOULD provide the protection for which it is intended,
> > namely protection against electric shock in the event of
> > a failure of some sort from mains to ground!
> > 
> > When it fails, hopefully its impedance is sufficiently 
> > low so as to cause the operation of an overcurrent device
> > (e.g, fuse or circuit-breaker).  Hopefully, the operator
> > will notice that the circuit-breaker has tripped and the
> > unit is taken out of service for repair.  
> > 
> > If the unit is not taken out of service, but moved to a
> > site where there is no ground, then the unit will indeed
> > be hazardous, with mains applied to the chassis through
> > the shorted suppressor.  This is the sequence of events
> > that would lead to a shock hazard.  
> > 
> > Evaluation of products for safety does not include moving
> > a unit (with a single fault) from a grounded state to an 
> > ungrounded state.
> > 
> > Note that, in every product, we PRESUME failure of basic 
> > insulation.  Grounding is one scheme for mitigating the 
> > failure of basic insulation.  What is the logic -- or
> > engineering basis -- for permitting grounding as a mitigator 
> > for failure of basic insulation but not for failure of a 
> > surge suppressor?
> > 
> > I submit that not allowing a surge suppressor from line 
> > to chassis because it is subject to shorting and causing 
> > a shock is nonsense.
> > 
> > Nevertheless, the various certification houses indeed 
> > have rules prohibiting surge suppressors from line to
> > chassis.  Their justification is that the failure of the 
> > surge suppressor WILL cause a shock hazard.  The construction
> > is DEFINED as hazardous.  No amount of engineering evaluation 
> > or testing is going to change the certification house rules!
> > 
> > 
> > Best regards,
> > Rich
> > 
> 
> ---------
> This message is coming from the emc-pstc discussion list.
> To cancel your subscription, send mail to [email protected]
> with the single line: "unsubscribe emc-pstc" (without the
> quotes).  For help, send mail to [email protected],
> [email protected], [email protected], or
> [email protected] (the list administrators).
> 

---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to [email protected]
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to [email protected],
[email protected], [email protected], or
[email protected] (the list administrators).

Reply via email to