SBC requires all equipment to meet the requirements of their TP76200MP
document dated July 1998.   In Section 8, there is a grouping of tests taken
from ANSI T1.315-1994 that requires proper operation of equipment from
-42VDC to -56.5 VDC over the expected life of the equipment.  There is a
short term requirement for proper operation at -40VDC for one minute and at
-75VDC for 10mS.  There is a battery drop out test in which the equipment
must recover and not be damaged when the input battery voltage is 0VDC for
5mS.  There is also a requirement to determine at what battery voltage the
equipment will be damaged (if it can be damaged).

SBC requires this information in the form of a test report.

Hope this helps,  
Jim

Jim Wiese
Compliance Engineer
ADTRAN, INC.
901 Explorer Blvd.
P.O. Box 140000
Huntsville, AL 35814-4000
256-963-8431
256-963-8250 fax
[email protected] 

> ----------
> From:         Dwight Hunnicutt[SMTP:[email protected]]
> Sent:         Wednesday, July 07, 1999 7:48 PM
> To:   TREG Newsgroup; NEBS Newsgroup; EMC PSTC
> Subject:      TR-NWT-00406 battery range
> 
> Anyone been required to guarantee that their equipment must operate 
> "for office battery range as per TR-NWT-000406"?
> 
> I assume this means your equipment will operate in a DC supply range per
> TR-406.  Anyone know the range?  thanks
> 
> D
> -- 
> ___________________________
>   DWIGHT HUNNICUTT
>   Sr. Compliance Engineer
>   VINA Technologies, Inc.
> 

---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to [email protected]
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to [email protected],
[email protected], [email protected], or
[email protected] (the list administrators).

Reply via email to