But what about permanently connected products?

-----Original Message-----
From: Rich Nute [mailto:[email protected]]
Sent: Friday, December 03, 1999 8:53 AM
To: Mavis, Robert
Cc: [email protected]
Subject: Re: AC Mains Color Coding





Hi Robert:


>   Yes certain UL standards have accepted the Lt Blue for the neutral. But
>   therein lies the conflict. The NEC states that the neutral (grounded
>   conductor) must be white or nat. Gray.  Has there been an acceptance by
the
>   NEC for the blue neutral??

Yes, the NEC does indeed accept blue for 
the neutral color for cords, but not for
building wiring.  See: 

Cords:  NEC Articles 200(c), 400-22(c), 400-23.
Buildings:  NEC Articles 200-7, 210-5.

Specifically, 400-22(c):

    "For jacketed cords furnished with 
    appliances, one conductor having its
    insulation colored light blue..."

(UL would not accept blue unless the NEC
first accepted blue.)


Best regards,
Rich



---------