Changing the thread of this topic a little, the US NFPA (National Fire
Protection Association) has a proposal for change regarding metrication
of the National Electrical Code (NEC). This is sponsored by the NEC
Technical Correlating Committee, at the direction of the NFPA Standards
Council, so I would expect it to be approved.

It is a mix of hard and soft conversions. Essentially it means all
dimensions in the code will be printed in SI metric units, occasionally
with inch-pound units in parenthesis. Conversion will be done with
appropriate rounding in the appropriate direction.
Trade size references for conduit will be converted to metric without a
physical change in size. The original trade sizes didn't actually mean
anything, for example 1/2 inch (rigid) conduit was actually 0.840"
outside, 0.636 inside, and other grades had no 0.500 applicable
dimension either. As a result, the trade name for 1/2 inch conduit will
become 16 mm conduit. The trade size is roughly an underestimate of the
internal diameter.

Note that wire size (AWG) and horsepower (motor sizes) will not be
converted (unfortunately).

Getting back to the RE: Update on UK conduit entry dimensions,
In North America, conduit or tubing is terminated in a variety of ways
including
- Threaded openings - mostly in castings
- Sleeve type terminations - for electrical metallic tubing (EMT), held
with set screw or clamp
- Sleeve type glued terminations - for plastic conduit
- Compression type terminations - for EMT and assorted flexible tubings
- Holes in sheet metal - for threaded connections with nuts on either
side
- Knockouts - sheet metal holes where the opening is still blocked by
metal ready to be punched out
- Fittings - adapting sleeve, glued, clamped or other terminations to
threaded holes or holes using nuts.
Note that the knockout or hole size is the parameter of most interest to
equipment manufacturers since they are making the termination for the
conduit, not the conduit.

Below is a table of North American conduit sizes you might find of use.
I was surprised to find there was such a thing as 1/4 and 3/8 conduit.
It is only for use in special circumstances.
I haven't provided actual conduit dimensions since these are different
depending upon type, e.g. rigid, IMT, EMT, flexible, corrosion
resistant, plastic, aluminum, etc. and even depending on manufacturer.
Note again, the trade size is not a real dimension found anywhere. The
knockout dimension is a real diamenter.

 Trade         Knockout

 inch   metric inch     metric

 1/4

 3/8    12

 1/2    16     7/8      23

 3/4    21     1-3/32   29

 1      27     1-11/32  35

 1-1/4  35     1-11/16  43

 1-1/2  41     1-15/16  50

 2      53     2-3/8    60

 2-1/2  63     2-7/8    73

 3      78     3-1/2    90

 3-1/2  91     4        100

 4      103    4-1/2    115

 5      129    5-5/8    127

 6      155    6-5/8    150

The North American knockout sizes already appear in IEC 60950 in metric
units (in parentheses). I am on TC74 WG8, but what should be done to
upgrade table 3A for Europe and the rest of the world should probably be
proposed by Cenelec. I would think that, like North American knockout
sizes, the dimension should represent the hole size needed for
connection of the conduit to the box, not necessarily any diameter of a
particular type of conduit or tubing. I have yet to see any of the
European inputs mention standard European conduit opening sizes rather
then conduit dimensions.


Jim Eichner wrote:

From:         Jim Eichner
<[email protected]>                                       Tue 1:28
PM
 Subject:        RE: Update on UK conduit entry dimensions
To:         [email protected]
Thanks for the update.  The final outcome of this thread seems to be
that the requirements in EN60950 are out of date.  Clause 3.2.2 insists
that permanently connected equipment, if it does not have a power, must
be provided with either a cable entry or conduit entry.  For the normal
3-wire supply circuit of 16A or less, the conduit entry must be
"suitable for" conduit with 16mm OD (Table 10).   The sources that we've
heard from are saying that 16mm OD conduit has become almost
unavailable, and everyone is using the next size up, which has 21mm OD
(not the 20mm listed in Table 10).
I'd like to hear from anyone on one of the xxx950 committees on this
subject.  Are we really discovering an anachronism in the standard, and
if so can something be done about it?
Thanks,
Jim Eichner