Hello Duncan and group,

If your equipment is in the scope of EN 60950 (IEC 60950) or UL 950,
than it depends of the power source feeding it

The matters around FIRE ENCLOSURES are dealt with in paragraph 4.4.5


No Fire enclosure required for

Par  4.4.5.2  3th       components in a SECONDARY CIRCUIT supplied by a
LIMITED POWER SOURCE and
                        mounted on a V-1 Class PCB
                                ...
A LIMITED POWER SOURCE (2.11) is the mains power supply secondary supplying
your circuit when it's power
is limited by an inherent way of protection (fuse) and less then 250 VA  or
protected by impedance and less then 100 VA.  Some voltage and other
restrictions exist.
This power supply NEEDS the use of an ISOLATING TRANSFORMER.

This implicates that the full primary circuit  must be contained into a FIRE
ENCLOSURE (4.4.4.1)
because the clause of 4.4.5.2. needs the ISOLATING TRANSFORMER (which is not
available in the primary)
The only parts that are fed by mains and need no FIRE ENCLOSURE are a MOTOR
or WIRING

This is why SMPS in ITE need to be completely encapsulated and open frame
SMPS are not allowed.

Nevertheless, many SMPS manuf's label their open frame  supplies as 950
compliant. They can't ,unless
you are prepared to change your entire ITE into a compliant FIRE ENCLOSURE.

This is a major pitfall in most ITE equipment in our test house !!


The exact formulation is more complex , so read the stuff.




Regards,

Gert Gremmen Ing.

== Ce-test, Qualified testing ==
Consultants in EMC, Electrical safety and Telecommunication
Compliance tests for European standards and ce-marking
Member of NEC/IEC voting committee for EMC.
Our Web presence: http://www.cetest.nl
List of current harmonized standards http://www.cetest.nl/emc-harm.htm
15 great tips for the EMC-designer http://www.cetest.nl/features01.htm



-----Original Message-----
From:   [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent:   vrijdag 24 september 1999 19:23
To:     [email protected]
Subject:        LCD Displays


I have a product that has an LCD display with an Inverter that operates at
100Khz 2KV and I believe is capable of supplying 6.5mA The question is does
it
require a fire enclosure?
If it does what are the requirements for the flamability of the screen and
any
plastic protective covers fitted to it. The screen is quite large, about the
size of a laptop PC screen. Perhaps some laptop PC manufacturers might have
some
ideas? are there any other things I must consider when using such a device
apart
from, obviously, insulation of the HT.
Regards,
    Duncan.


---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to [email protected]
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to [email protected],
[email protected], [email protected], or
[email protected] (the list administrators).



---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to [email protected]
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to [email protected],
[email protected], [email protected], or
[email protected] (the list administrators).

Reply via email to