As usual Egon, you are correct we have abandoned are old 25 Amp tester and
created a new fixture to allow us to do the continuity tests at twice the
rating of the branch protection, 30,40 or 60 Amps. We tried many different
approaches and quoted many different standards but this issue is one that UL
and CSA will not budge on. You may get by at 25 if you list under UL1950
Second Edition for U.S. only but third edition or a C-UL mark will have you
testing at 30 Amps or twice the rating of the branch protection. Also UL
does not consider supplementary protector ratings as applicable, so if you
want to base your test current on inherent devices in the equipment you have
to make sure the protection device is listed to the proper UL standard. 

By the way, CSA 0.4 is required not only in Canada, but also in the 
US.  Since both countries have adopted the same binational CSA950/UL1950 
standard, and since CSA 0.4 is specifically required by this standard, this 
has become an official requirement for the US.  This is an unequivocal 
requirement, so I have no doubt that all US safety agencies are diligently 
performing the CSA tests.


Monty Griffith
Senior Product Safety Engineer
EMC Quality Manager
Intergraph Compliance Services
Ph. (256) 730-6017
Fx. (256) 730-6239
http://cscsrv.ics.ingr.com


---------