[email protected] writes:
>Dear All,
>
>Question 1: Can we rely on the two screws securing the appliance  inlet
>as a means for bonding? Over the years, I have been told by  various
>safety agencies that such construction is unacceptable.

Over the years I, too, have been told that the metal part provided as part
of the appliance inlet was not acceptable and that I would have to make a
specific ground to a specific attachment point, i.e. "the stud". The only
explanation I recall is that the screws holding the appliance inlet may
loosen (or be loosened) thus inadvertently losing the ground connection,
whereas if the earth terminal is taken to a specific point where it is the
first or only connection, then you must take a specific and intentional
action to disconnect earth from  the equipment. And, that first point of
earth ground is protected with lockwashers and its own nut. Other grounds
may be stacked on top of that, but it must have "its own means of
securement".
>
>Question 2: Am I correct in assuming that the appliance earthing 
>terminal for the above Listed/Certified products was considered as  the
>main protective earthing terminal? 

Yes.
>
>Question 3: Why do most other ITE manufacturers use the "stud  on the
>chassis method" for protective earthing terminal?
>
See my answer to #1. It was easier to give "them" a "stud" and not argue
about it. It carries onward to this day. In retrospect, I don't mind it
actually. It makes it clear that there is a specific point of earth ground
in a system. 
>
>
>
>PETER S. MERGUERIAN

Regards,
Scott
[email protected]


---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to [email protected]
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to [email protected],
[email protected], [email protected], or
[email protected] (the list administrators).

Reply via email to