Regards,

Gert Gremmen Ing.

== Ce-test, Qualified testing ==
Consultants in EMC, Electrical safety and Telecommunication
Compliance tests for European standards and ce-marking
Member of NEC/IEC voting committee for EMC.
Our Web presence: http://www.cetest.nl
List of current harmonized standards http://www.cetest.nl/emc-harm.htm
15 great tips for the EMC-designer http://www.cetest.nl/features01.htm



-----Original Message-----
From:   Ing. Gert Gremmen [mailto:cet...@cetest.nl]
Sent:   maandag 15 maart 1999 19:35
To:     Peter Merguerian
Subject:        RE: Earth Bonding Requirements for Telecom Equipment
Importance:     High

Hello Peter,

I am not familiar with your bullet type wire termination, at least not under
that name,
so i cannot share my experience with these.

About the termination of earth wires; no i know that it's no good  practice
and it
is therefore not allowed in 950.  You better bond the two together on
a separate bonding terminal and then lead one wire to your 5-pole connector.

Even better for reliability is two 3-pole connectors.

The main problem with 2 wires in one (crimp) type of connector is that if
one of the 2 supply wires is
pulled away by brute force, that the other wire goes with it, or if it's
not, its connection quality is reduced
below acceptable.  This certainly reduces the quality of your design, where
you used
a second redundant supply cable for reliability reasons, you invalid it's
redundancy
by connecting the two together.

I certainly disagree using a shield for safety. One might conclude that
shielding is
superfluous and replace by unshielded, thereby invalidating the safety
concept.

Only one solution is acceptable : the right one ;<).

In general: safety measures should be visible, and clearly distinguishable
from functional
circuits, and should never be hidden as a functional circuit.

visible : for inspection in manufacturing and quality control
clearly as such : so no one in the field might be tempted to replace a
unclear measure by a less reliable "equivalent"


Regards,

Gert Gremmen Ing.

== Ce-test, Qualified testing ==
Consultants in EMC, Electrical safety and Telecommunication
Compliance tests for European standards and ce-marking
Member of NEC/IEC voting committee for EMC.
Our Web presence: http://www.cetest.nl
List of current harmonized standards http://www.cetest.nl/emc-harm.htm
15 great tips for the EMC-designer http://www.cetest.nl/features01.htm



-----Original Message-----
From:   owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org] On Behalf Of Peter Merguerian
Sent:   zondag 14 maart 1999 21:57
To:     'EMC-PST'; t...@world.std.com
Subject:        Earth Bonding Requirements for Telecom Equipment

Dear All,

A telecom rack subsystem has two power entry modules (for
redundancy); two cables, one for each power entry module, each
consisting of 3 leads (+, - and earth), are terminated by means of a
3-pole connector to each power entry module; the other end of the
cables are terminated to one 5-pole connector where two of the
earthing leads are terminated together in one terminal of the
connector and the other four leads (supply) are terminated to each
of the remaining terminals of the connector. This 5-pole connnector
is the connection to the power distribution unit which has the main
earthing terminal, power supply connections and circuit breakers.

1. Do you see a problem with UL1950/EN 60950 of terminating two
earth bonding leads to one terminal? I should state that the
connector is Recognized but most likely evaluated to accept one
wire per terminal.

2. Assuming that the combination of connector and two leads in
one terminal was submitted for a separate investigation (to one of
the connector standards), is there some clause in the standard
which will not allow me to use this type of termination?

3. In lieu of 3 leads/cable, can manufacturer use 2 leads/cable and
use the shield of the cable as the earth bonding "conductor"?

4. For wire terminations in general, I find that more and more
manufacturers like (for manufacturing reasons) to terminate their
leads to insulated bullet type pressure terminal connectors prior to
terminating them to connectors and/or terminal blocks employing
pressure wire terminals. However, even though the
connectors/terminal blocks are Recognized, these bullet type
connectors are not Approved.

Is anyone using the same technique in manufacturing? If so, do
you use Listed and/or Recognized bullet-type pressure wire
connectors? If so, can you supply with some manufacturer's
names of such connectors?


Thanks in Advance,





PETER S. MERGUERIAN
MANAGING DIRECTOR
PRODUCT TESTING DIVISION
I.T.L. (PRODUCT TESTING) LTD.
HACHAROSHET 26, P.O.B. 211
OR YEHUDA 60251, ISRAEL

TEL: 972-3-5339022
FAX: 972-3-5339019
E-MAIL: pe...@itl.co.il
Visit our Website: http://www.itl.co.il

---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).

Reply via email to