Hi Jeff:


Quotes from the 1996 NEC:

"110-2.  Approval.  The conductors and equipment required 
or permitted by this Code shall be acceptable only if 
approved."

"Approved:  Acceptable to the authority having jurisdiction."

"90-7.  Examination of Equipment for Safety.  For specific
items of equipment and materials referred to in this Code, 
examinations for safety made under standard conditions will
provide a bais for approval where the record is made 
generally available through proumlgation by organizations
properly equipped and qualified for experimental testing,
inspections of the run of goods at factories, and service-
value determination through field inspections.  This avoids 
the necessity for repetition of examinations by different
examiers, frequently with inadequate facilities for such
work, and the confusion that would result from conflicting 
reports as to the suitability of devices and materials
examined for a given purpose.

"It is the intent of this Code that factory-installed 
internal wiring or the construction of the equipment need
not be inspected at the time of installation of the equipment, 
except to detect alterations or damage, if the equipment has 
been listed by a qualified electrical laboratory that is 
recognized as having the suitable facilities described above 
and that requires suitability for installation by this Code."

So, the NEC requires all parts to be certified.

If the rack has a certification label on it indicating the
whole thing is certified, then the inspector will stop
there.  If the rack does not have such a label, then the
inspector is entitled to look at the individual parts 
included in the rack for certification labels.

It is true that a power supply can be evaluated as a
component of the system.  If this is the case, then the
system must bear a certification label.  If the inspector
does not accept that the power supply is included in the
system certification, then providing him with a copy of
the certification report will clarify that problem.


Best regards,
Rich



-------------------------------------------------------------
 Richard Nute                      Product Safety Engineer
 Hewlett-Packard Company           Product Regulations Group 
 AiO Division                      Tel   :   +1 619 655 3329 
 16399 West Bernardo Drive         FAX   :   +1 619 655 4979 
 San Diego, California 92127       e-mail:  [email protected] 
-------------------------------------------------------------







---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to [email protected]
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to [email protected],
[email protected], [email protected], or
[email protected] (the list administrators).

Reply via email to