When systems are tested using these techniques, make sure the latest
version of EN61000-3-2 is used, incorporating Ammendment 14.

Previously, simple techniques could be used to modify the input
current waveform, and distort it outside the 'special waveform'
envelope shown in figure 1 of the standard.
This enabled you to use the less-stringent Class A limits.

With the incorporation of Ammendment 14, there is no evaluation of the
input current waveform to determine the test limit.  The application
alone will determine the test limit used.

----
Patrick Lawler
[email protected]


On Tue, 12 Dec 2000 10:03:50 +1100, Jon Keeble
<[email protected]> wrote:
>You may be interested in a paper 
>
>Power Factor Correction for AC-DC Converters with Cost Effective Inductive
>Filtering
>
>by 
>
>W.Wölfle Convertec Ltd., Wexford, IRELAND
>W.G.Hurley National University of Ireland Galway, IRELAND 
>S.Arnold Enserb Bordeaux, FRANCE
>
>To quote the conclusion:
>
>This paper presents a new, simple and cost effective solution
>for the power factor correction of the input current of a
>switch mode power supply, which meets the IEC limits on
>harmonic distortion. A sloped air-gap inductor, which adapts
>its inductance values to the input current conditions of the
>power supply, is used to shape the current to comply with the
>limits for harmonic distortions as defined in EN61000-3-2.
>
>It is shown that using a classical inductor design, the filter
>inductor is too bulky, whereas the volume of the sloped air-gap
>choke is as small as the switching transformer of the
>power (e.g.100 kHz) supply. In fact, the volume required is
>not bigger then that required for an active PFC circuit, but at
>a fraction of the cost.
>
>The .pdf is too large to post, but I'll mail a copy to the first ten
>callers ...
>
>Seasonal Greetings
>
>-----------------------------
>Jon Keeble          
>Fairlight
>Hardware Engineering Manager
>8977 9931
>[email protected]


-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Jim Bacher:              [email protected]
     Michael Garretson:        [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]

Reply via email to