I'm sure we have been through this all before, but here goes : For equipment certified by UL and CSA (and I assume by other agencies, but I have no personal experience), the End of Line Tests will be specified as part of your certification.
For Europe, there is EN 50116, which "defines the routine electrical safety tests and their procedures to be applied during or after the manufacturing process of equipment certified or declared as complying with EN 60950." This requires the Earth Bonding Test at 1.5 times the current capacity of the circuit, but not more than 25A, with the 0.1 ohm limit, and an electric stregth test of 1500V ac or the dc equivalent, for basic insulation, and 3000V or the dc equivalent for reinforced insulation, with the proviso that "testing of components connected between the primary and secondary circuits shall be performed before final assembly". (i.e. it is ok to use power supplies where the transformers, etc, have been 100% tested at 3000V). There is no Insulation Resistance Test specified, and I am unaware of any such requirement for IT products. Regards, John Crabb, Development Excellence (Product Safety) , NCR Financial Solutions Group Ltd., Kingsway West, Dundee, Scotland. DD2 3XX E-Mail :[email protected] Tel: +44 (0)1382-592289 (direct ). Fax +44 (0)1382-622243. VoicePlus 6-341-2289. > -----Original Message----- > From: Tony Reynolds [SMTP:[email protected]] > Sent: 29 November 2000 11:02 > To: [email protected] > Subject: End of Line Testing of IT Equipment > > > All, > > What are the exact requirements for End of Line testing and do they > differ from country to country. We currently subject products to the > > following tests: > > 1. Earth Bonding at 25A (resistance to be less than 0.1 Ohms) > > 2. Dielectric strength test of 2.1KVDC for 2 seconds. > > 3. Insulation resistance test of 500VDC (resistance to be greater > than > 10MOhms). > > Question > -------- > > Is this last test mandatory for product compliance in > UK/Europe/USA/Rest of the World? > > > Kind Regards > > Tony Reynolds > Principal Compliance Engineer > Pitney Bowes Ltd > The Pinnacles > Harlow > Essex > CM19 5BD > Tel +44 1279 449479 > Fax +44 1279 449118 > E-Mail: [email protected] > www.pitneybowes.com > ------------------------------------------- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. To cancel your subscription, send mail to: [email protected] with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Jim Bacher: [email protected] Michael Garretson: [email protected] For policy questions, send mail to: Richard Nute: [email protected]