UL 498 covers attachment plugs and receptacles and section 114 gives the
specifics on the plug retention tests.  For UL, retention is tested with a
whole plug and there is no requirement for testing each pole separately in
this standard.  If the receptacle is designed for either a two wire or
three wire plug, it must be tested with both.

For non-locking receptacle, the plug must be held in place by a pull of no
less than 3 pounds force (13 N).  It must release with a pull of no more
than 15 pounds force (67 N).  This test is not applied to locking
receptacles.

Ted Eckert
Regulatory Compliance Engineer
American Power Conversion Corporation
[email protected]

The items contained in this e-mail reflect the personal opinions of the
writer and are only provided for the assistance of the reader.  The writer
is not speaking in an official capacity for APC nor representing APC's
official position on any matter.


                                                                                
                                                
                    [email protected]                                               
                                                
                    m                    To:     [email protected]              
                                                
                    Sent by:             cc:                                    
                                                
                    owner-emc-pst        Subject:     CSA C22.3 #42-99          
                                                
                    [email protected]                                               
                                                   
                                                                                
                                                
                                                                                
                                                
                    11/09/00                                                    
                                                
                    11:53 PM                                                    
                                                
                    Please                                                      
                                                
                    respond to                                                  
                                                
                    rbusche                                                     
                                                
                                                                                
                                                
                                                                                
                                                





I had a question posed to me by a fellow engineer with regard to the design
of an electrical outlet to be used in ITE equipment. He is following the
requirements identified in CSA standard C22.2  #42-99 where each pole and
ground pin is individually subjected to a weighted pullout test. The
question was whether or not this is also part of the equivalent UL
requirements for electrical outlets. An engineer from a reputable power
cord
manufacturer told him that UL did not require this test.  Unfortunately I
have no expertise with either standard and could not help. Could someone
let
me know what the equivalent UL standard is and whether this is a true
statement.

If someone could contact me off line I would appreciate it.

Thanks in advance...

Rick Busche
[email protected]

-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Jim Bacher:              [email protected]
     Michael Garretson:        [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]






-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Jim Bacher:              [email protected]
     Michael Garretson:        [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]

Reply via email to