forwarding for [email protected]

____________________Forward Header_____________________
Subject:    FW: UL1950 - Clause 2.5.5
Author: "  Peter Tarver   <[email protected]>"
List-Post: [email protected]
Date:       11/7/00 1:25 PM



-----Original Message-----
From: Tarver, Peter [SC1:9031:EXCH] 
Sent: Tuesday, November 07, 2000 7:42 AM
To: [email protected]
Subject: RE: UL1950 - Clause 2.5.5


Imagine my surprise that an NRTL is asking this question ;>

Since the product is only intended for sale in the US, the NEC accepts green
insulated equipment grounding conductor insulation in power supply cords
[refer to USNEC Section 400-23(b)] and considering that UL wouldn't turn
away a client for US only certification that used a Listed cordset, it
shouldn't be a big issue for you, either.  Perhaps you can make mention of a
relaxation of the requirement in your descriptive report, citing the NEC
reference.

BTW, I've cut open cords and found green/yellow insulation on the earthing
conductor.

Regards,

Peter L. Tarver, PE
[email protected]


-----Original Message-----
From: Loop, Robert [mailto:[email protected]]
Sent: Monday, November 06, 2000 7:53 AM

Group,

We are looking at a Class 1, cord connected product that utilizes a NEMA
5-15P plug on one end and is wired to a non-service accessible terminal
block in the rear of the unit with a Recognized compression fitting for
strain relief.  The product is being evaluated against UL1950.

Here's the problem:

The manufacturer only wants to sell the product in the USA and is using a UL
listed cordset with US color code (black/white/green).  Clause 2.5.5
requires that the ground wire be bare or green with a yellow stripe.  They
have expressed an unwillingness to change out the cordset claiming ( in
which my experience agrees) that no one sells a cordset with
black/white/green-yellow color code. 

In order to meet the letter of the clause, we could require them to strip
the 1-1/2 " portion of the green wire that extends past the outer jacketing,
but it seems like a backhanded way of meeting the Clause (does the bare wire
make the product any safer?).

I remember some clause in 1950 making reference to installing the product
"in accordance with the national wiring rules", but can't seem to locate it.
If that's the case, and the NEC does recognize the black/white/green color
code, what's the best answer to resolve this?

Your engineering expertise and enlightenment is always welcomed.


Sincerely,
Robert Loop
Engineering Supervisor
Wyle Laboratories 
Product Safety
ph - (256) 837-4411 x313
fax- (256) 721-0144
e-mail: [email protected]

-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Jim Bacher:              [email protected]
     Michael Garretson:        [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]

Reply via email to