Hi Robert.

Here's a suggestion that may/may not be good for you . . . 

I needed to have cable ingress/egress through the bottom of a telco cabinet
in addition
to allowing for ventilation and yet still meet UL 1950 & EN 60950.

What I did was sacrifce a couple of rack units at the bottom of the cabinet
and create
a 'baffle'. We had a large rectangular hole in the bottom of the cabinet. We
took a
piece of perforated stock (approx. 63% opening) and had it angled up about
3 inches toward the rear, with the rear overlapping the closed section of
the bottom
by an inch (there were sides to the baffle as well). We also had a 'lip' on
the
bottom plate surrounding the openings so that if 
a 'fluid' of some sort were to hit the plate, it was contained by the lip
and could not
flow out of the opening.

If you'd like a sketch, contact me directly.

John A. Juhasz
Product Qualification &
Compliance Engineer

Fiber Options, Inc.
Bohemia, NY 11716  USA

Tel: 631-419-2324 (direct)
 


-----Original Message-----
From: Robert Legg [mailto:[email protected]]
Sent: Monday, November 06, 2000 8:30 AM
To: IEEE EMC-PSTC Forum
Cc: athome Legg
Subject: Hot Flaming Oil/ applicability in 60950




Group,

The ventilation hole pattern on the bottom of Telecom Rack assemblies seems
to have been adopted from older standards. This was to address the safety
of assemblies that might use less-than-94V-0 flammability-rated materials,
including unfilled thermoplastics, resins, insulating oils, varnishes and
other potential fuels.

These are materials that are avoidable at the present time, without serious
cost implications.

The ventilation pattern permitted by the requirement is highly restrictive
in its effects on ventilation, limiting the power density that is
achievable without the use of unreliable air movers.

Is it possible to establish safe practice, in dedicated rack assy's, when
using more practical ventilation patterns? This could perhaps be achieved
by reporting oxygen index limits of the components and materials enclosed.
If you can't set it on fire with a flame thrower, then obviously it doesn't
pose that risk to its surroundings.

Rob Legg
Tectrol Inc
[email protected]


-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Jim Bacher:              [email protected]
     Michael Garretson:        [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]

Reply via email to