Hi John, I agree there are many different mains wiring configurations, I was merely pointing out the case where I believe a 2 pole circuit breaker is required. How do you handle 230V equipment marketed worldwide, that may encounter any number of these configurations?
Ray Russell [email protected] -----Original Message----- From: Wagner, John P (John) [mailto:[email protected]] Sent: Monday, October 09, 2000 10:28 AM To: 'brian_kunde'; emc-pstc; 'Russell, Ray' Subject: RE: Overcurrent Protection: One or Both Sides? I take some exception to the response below. Single phase connections between phases either on a delta or wye system do not have a neutral connection. There are two grounded delta systems -- corner ground where one phase is grounded, or center tapped ground on one of the phases (commonly called high leg). There are also variations of the grounding scheme to allow for impedance grounded systems where appropriate. A standard two pole breaker os not designed, nor can it be used to interrupt neutral. For that, a special shunt trip braker is needed. John P. Wagner AVAYA Communication 11900 N. Pecos St, Room 2F58 Denver CO 80234 email: [email protected] phone: 303 538-4241 fax: 303 538-5211 > ---------- > From: Russell, Ray[SMTP:[email protected]] > Reply To: Russell, Ray > Sent: Monday, October 09, 2000 5:15 AM > To: 'brian_kunde'; emc-pstc > Subject: RE: Overcurrent Protection: One or Both Sides? > > > Hi Brian, > > I see most of the return postings have focused on the UK, which has a > terminated neutral system. There are several installations especially in > the > US, where the power could be derived from a delta, or unterminated neutral > system. I believe in this case, overcurrent protection is required on both > lines. In addition, the 2 pole circuit breaker method provides a suitable > 2 > pole disconnect. > > Good Luck, > > Ray Russell > [email protected] > > -----Original Message----- > From: brian_kunde [mailto:[email protected]] > Sent: Friday, October 06, 2000 12:32 PM > To: emc-pstc > Subject: Overcurrent Protection: One or Both Sides? > > > > > The issue of designing in Overcurrent Protection on one side or both sides > of > the AC mains keeps coming up. We deal in Laboratory Equipment so the EN > 61010-1 > is the standard we use. I'm not sure what EN60950 would say on the > subject. > > The only area I have found that deals with this question is a NOTE in > section > 9.6 of EN61010-1 which says, "Overcurrent protection devices (e.g. fuses) > should > preferably be fitted in all supply conductors." > > This seems "GRAY" to me and I get beat up on it all the time. I feel that > overcurrent protection should be on all current carrying conductors. With > a > 230V~ product you never know where in the world the product will be > shipped, > if > the AC Main has a grounded neutral, or if the receptacle is polarized. > So, > I > feel you never know for sure which line or if both lines will be "HOT" in > reference to Earth ground. > > If my thinking is correct, shouldn't ALL 230V~ products have overcurrent > protection on both sides of the line? I would think so, but I see > products > everyday that only have ONE side of the line fused. My superiors feel > that > if > others can get away with it, why can't we. Why add the extra cost of > double > pole breakers or double fuse holders if it is not necessary? > > Am I being too cautious or do I have a point? > > Thank you for your support and advice. > > Brian Kunde > LECO Corp. > > > > ------------------------------------------- > This message is from the IEEE EMC Society Product Safety > Technical Committee emc-pstc discussion list. > > To cancel your subscription, send mail to: > [email protected] > with the single line: > unsubscribe emc-pstc > > For help, send mail to the list administrators: > Jim Bacher: [email protected] > Michael Garretson: [email protected] > > For policy questions, send mail to: > Richard Nute: [email protected] > > > ------------------------------------------- > This message is from the IEEE EMC Society Product Safety > Technical Committee emc-pstc discussion list. > > To cancel your subscription, send mail to: > [email protected] > with the single line: > unsubscribe emc-pstc > > For help, send mail to the list administrators: > Jim Bacher: [email protected] > Michael Garretson: [email protected] > > For policy questions, send mail to: > Richard Nute: [email protected] > > ------------------------------------------- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. To cancel your subscription, send mail to: [email protected] with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Jim Bacher: [email protected] Michael Garretson: [email protected] For policy questions, send mail to: Richard Nute: [email protected]