Current editions of UL 1950/CSA 22.2 No. 950 (3rd Ed) and EN 60950 (2nd Ed
4th Amd) would require BASIC INSULATION (see 6.2.1.2) between TNV-2 & SELV.

I believe that a working voltage of 150VDC (Max TNV + some left over on SELV
side) and 200Vpk (ringing) is generally accepted as the working voltage
between TNV-2 & SELV.  At least this works for the labs I talk to. (UL is a
bit different here, as TNV limits are lower).  150VDC would determine
CREEPAGE DISTANCE, 200Vpk CLEARANCE:

Table 6:  (CREEPAGE, 150VDC, MG III) = 1.6mm - for the US this may be
reduced to 1.5mm as the TNV limits are lower.
Table 5:  (CLEARANCE, 200Vpk, PD 2) = 0.9mm (Mains supply < 150Vrms)
Table 5:  (CLEARANCE, 200Vpk, PD 2) = 1.0mm (150Vrms<Mains Supply<300Vrms)

As Helmut indicated below, BASIC INSULATION (clause 6.2.1.2) may not be
required if your SELV ckt has a PE connection...but this, of course, may not
be acceptable in all countries...

Also, I do not know that anyone (CB's at least) is testing to IEC 60950 yet?
Let me know if I'm wrong on this..

Regards,

Mel Pedersen, Midcom Inc.
mailto:[email protected]


-----Original Message-----
From: [email protected] [mailto:[email protected]]
Sent: Friday, June 16, 2000 1:34 AM
To: [email protected]; [email protected]
Subject: AW: TNV-2 to SELV Spacing


Gary,
between TNV2 and PE (ground) the only requirement is functional insulation.

For max TNV2 (120Vdc) the following spacings apply:
clearance:      0,6mm (table 2K last column)
creepage:       0,6 up to 2,4mm depending on the PD and MG
                (table 2L)
                eg for PD 2 MG IIIa 1,5mm
relevant document: IEC 60950 3.ed 1999
best regards
helmut hintz

----------
Von: Gary.McInturff / unix ([email protected])
An: [email protected]
Betreff: TNV-2 to SELV Spacing
Datum: Donnerstag, 15. Juni 2000 16:44


        Temporarily without my standard, and need a spacing requirement.
Seems to me that over surface it was 1.4 mm or 1.0 mm through air, but it
also seems to me that it was contingent upon whether or not the secondary
was grounded or not. How about TNV-2 to ground?
        As always there is no room, no time and we need to spin the board.
        Thanks
        Gary

-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Jim Bacher:              [email protected]
     Michael Garretson:        [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]



-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Jim Bacher:              [email protected]
     Michael Garretson:        [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]


-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Jim Bacher:              [email protected]
     Michael Garretson:        [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]

Reply via email to