A little more on the grounding issue for Kelly.

Rich mentioned the problem can occur (voltage potential between different
grounds in a building) if the grounded service conductor(neutral) is
grounded at more than one location. This would certainly cause the problem.
That along with additional safety issues is why it is a violation of the
National Electric Code.

Keep in mind there are two different terms in use.
The grounded conductor (neutral) and the grounding conductor (equipment
ground). These two are only allowed to meet at one location. The service
equipment. There is another term "bonding" that is defined as the permanent
joining of metallic parts to form an electrically conductive path.

Note that there has been extensive rewriting of Article 250 of the National
Electric Code from the 1996 code to the 1999 code. Most language was put
into positive format to try and eliminate the multitude of exceptions.

Specifically 250-23 (1996), 250-24 (1999) require the service supplying a
building to have a grounding electrode connected to the grounded conductor.
A grounding connection shall not be made to any grounded circuit conductor
on the load side of the service disconnecting means. There are some
exceptions when there are multiple buildings served from the same service,
or separately derived systems involved (generators, etc.)

>From the service equipment (where outside power enters the building)
separate grounded and grounding conductors must be run. Throughout the
building additional bounding is allowed and mandated if the metal can become
energized in the event of a failure. This is to prevent "objectionable
current" from flowing on the grounding conductor. 250-21(b)(1996), 250-6(b)
(1999) allows alterations to stop "objectionable currents" Be careful
though, 250-21(d) (1996), 250-6(d) (1999), state that noise that results in
data errors is not considered to be "objectionable current".

Computer and communication gear may be sensitive to these stray currents.
Circulating currents on equipment grounding conductors, metal raceways, and
building steel develop voltage potentials. One way this has been addressed
in the past has been to isolate the equipment that is suffering from the
grounding system. However, this can create a shock and fire hazard and is
not an acceptable means for handling the problem.

Equipment that is at the end of long runs of the grounding conductor may see
a rise in voltage on the grounding. It is permissible to supplement the
grounding by bonding to building steel, raceways, or adding supplemental
ground rods. However, these are supplements and do not allow you to remove
the grounding conductor 250-51(1996). By bonding all equipment and metal in
a building wherever possible you can create a more equipotential ground
plane and hopefully eliminate the noise. Failing that, isolated grounding
runs are allowed to equipment by 250-74 exception no. 4 (1996), 250-146(d)
(1999).

John L. Allen, P.E.
Electrical Engineer
Engineering and Fire Investigations
4405 International Blvd. Suite B-115
Norcross (Atlanta), Georgia  30093-3013
Tele: 800-245-9601 in GA: 770-925-9600
Fax: 770-925-9649  Cell: 404-931-4481
Visit our web site at http://www.efiinfo.com



-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Jim Bacher:              [email protected]
     Michael Garretson:        [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]

Reply via email to