Richard,

I believe the concern is for products that are shipped with a junction box 
not a power supply cord.  For example, we approved a Kiosk that was 
provided with a junction box and no power cord.  The installer 
(electrician) was required to size the breaker and mains wiring.

Best Regards,

Jody Leber

[email protected]
http://www.ustech-lab.com

U. S. Technologies
3505 Francis Circle
Alpharetta, GA 30004

770.740.0717
Fax:  770.740.1508


-----Original Message-----
From:   [email protected] [SMTP:[email protected]]
Sent:   Friday, March 10, 2000 3:18 PM
To:     [email protected]
Subject:        Short-circuit Protection


According to Clause 1.7.11 of the 60950 clones, for equipment that is
permanently wired and relies upon the building installation for
short-circuit protection, ". . . the equipment installation instructions
shall so state and shall also specify the requirements for short-circuit
protection or over-current protection, where necessary, for both."

All certified beakers have a specified breaking capacity and the building
wiring is sized for that protection. I understand that the compliant
equipment's internal wiring, and where allowed, permanently connected power
cord will withstand the short-circuit currents allowed by the certified
external breakers. So, it is unclear to me that any additional
specifications, including a current rating, are required other than stating
that the protection is required.

What statements are you making in your instructions to comply with this
requirement?


-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Jim Bacher:              [email protected]
     Michael Garretson:        [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]


-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Jim Bacher:              [email protected]
     Michael Garretson:        [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]

Reply via email to