I'm not sure the NEC would regulate this stuff unless it was part of a new
construction occupancy inspection, even then they may quit looking as soon
as they see a NRTL mark, assuming they already did that part.
But that is somewhat outside the point. UL and the NEC work pretty much
hand-in-hand and when one changes the other changes as well. The NEC has
hired UL on occasion to perform long term tests as part of their process.
Bazillions of years ago I can remember seeing a years long aging test of
aluminum wire for home construction test, that was a partnership between the
two.
So I wouldn't expect there to be many differences in the issues we are
talking about regardless of who is doing the interpretation. But among other
things you need to point out to whomever that you intend it to be in a
higher than average ambient, or it will be investigate as if it were a 30C
ambient, and you will probably get a different answer.
Gary



                -----Original Message-----
                From:   Dick Grobner [mailto:[email protected]]
                Sent:   Friday, March 10, 2000 10:12 AM
                To:     '[email protected]'
                Cc:     '[email protected]'
                Subject:        FW: Correction factor for power supply
cords.




                -I agree with Ed's comment. Were mfg. of medical equipment,
thus within our
                "global" standard EN60601-1 Table XV provides a cross
reference between the
                conductors cross sectional area (mm sq. for copper)and the
rated current of
                the equipment. Also referring to UL 2601 (our US std) in the
"UL Deviations"
                too IEC 601-1 it doesn't reference the NEC. I'm not an
electrician (or an
                expert on the NEC)but would tend to say that the NEC would
not "regulate"
                this area but rather the appropriate product standard would.

                Hope this helps

                -----Original Message-----
                From: [email protected]
[mailto:[email protected]]
                Sent: Friday, March 10, 2000 9:12 AM
                To: Kelly Tsudama
                Cc: [email protected]
                Subject: Re: Correction factor for power supply cords.





                Kelly:
                The NEC is written to keep structures safe. Flexible cords
used in
                structures
                are normally used in free air.
                If you are using a flexible cord in equipment, you need to
rate its ampacity
                in
                accordance with whatever standard you are using. The NEC
relies on the NRTL
                label and testing for the safety of equipment.
                If you are using a flexible cord in a high ambient I would
contact the mfg
                for
                the appropriate derating.




                Kelly Tsudama <[email protected]> on 03/09/2000 09:33:14 PM

                Please respond to Kelly Tsudama <[email protected]>

                To:   [email protected]
                cc:    (bcc: Ed Rauch/MAIN/MC1)

                Subject:  Correction factor for power supply cords.






                Hi Group

                I am hoping that I can get your opinions with an issue
regarding the
                correction
                factor of power supply cords.  For instance, in the NEC
table 310-17, for
                single
                conductors in free air, there is a chart at the bottom of
the table that
                allows
                you to determine how to factor in the ambient temperature.
However, for a
                flexible power cord, the table 400-5 does not have any
correction factor
                table.

                At first I thought that this is because cords always have a
temperature
                rating
                marked on them, but then I recall that most (if not all)
single conductors
                have
                this marking too.... Is there a need to "de-rate" a power
cord's current
                rating
                based on the expected ambient temperature?  If so, where in
the NEC did I
                miss
                this fact?  If not, why not?

                Thanks for your help,
                Kelly

        
****************************************************************
                Kelly Tsudama
                Cisco Systems
                [email protected]
                408-527-0216
                408-525-9150 fax
                408-322-9024 pager

                -------------------------------------------
                This message is from the IEEE EMC Society Product Safety
                Technical Committee emc-pstc discussion list.

                To cancel your subscription, send mail to:
                     [email protected]
                with the single line:
                     unsubscribe emc-pstc

                For help, send mail to the list administrators:
                     Jim Bacher:              [email protected]
                     Michael Garretson:        [email protected]

                For policy questions, send mail to:
                     Richard Nute:           [email protected]









                -------------------------------------------
                This message is from the IEEE EMC Society Product Safety
                Technical Committee emc-pstc discussion list.

                To cancel your subscription, send mail to:
                     [email protected]
                with the single line:
                     unsubscribe emc-pstc

                For help, send mail to the list administrators:
                     Jim Bacher:              [email protected]
                     Michael Garretson:        [email protected]

                For policy questions, send mail to:
                     Richard Nute:           [email protected]


                -------------------------------------------
                This message is from the IEEE EMC Society Product Safety
                Technical Committee emc-pstc discussion list.

                To cancel your subscription, send mail to:
                     [email protected]
                with the single line:
                     unsubscribe emc-pstc

                For help, send mail to the list administrators:
                     Jim Bacher:              [email protected]
                     Michael Garretson:        [email protected]

                For policy questions, send mail to:
                     Richard Nute:           [email protected]
                

-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Jim Bacher:              [email protected]
     Michael Garretson:        [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]

Reply via email to