Kelly,

You derate the cord with respect to the ampacity allowed by the receptacle it
connects to.  Art. 210-23 of the NEC indicates that cord connected equipment can
draw no more than 80 % of the maximum receptacle rating.


Regards,

Wolf Josenhans




Kelly Tsudama <[email protected]> on 03/09/2000 09:33:14 PM

Please respond to Kelly Tsudama <[email protected]>

Sent by:  Kelly Tsudama <[email protected]>


To:   [email protected]
cc:    (Wolfgang Josenhans/MW/US/3Com)
Subject:  Correction factor for power supply cords.





Hi Group

I am hoping that I can get your opinions with an issue regarding the correction
factor of power supply cords.  For instance, in the NEC table 310-17, for single
conductors in free air, there is a chart at the bottom of the table that allows
you to determine how to factor in the ambient temperature.  However, for a
flexible power cord, the table 400-5 does not have any correction factor table.

At first I thought that this is because cords always have a temperature rating
marked on them, but then I recall that most (if not all) single conductors have
this marking too.... Is there a need to "de-rate" a power cord's current rating
based on the expected ambient temperature?  If so, where in the NEC did I miss
this fact?  If not, why not?

Thanks for your help,
Kelly

****************************************************************
Kelly Tsudama
Cisco Systems
[email protected]
408-527-0216
408-525-9150 fax
408-322-9024 pager

-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Jim Bacher:              [email protected]
     Michael Garretson:        [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]







-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Jim Bacher:              [email protected]
     Michael Garretson:        [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]

Reply via email to