One other question if I may, do you know how this will impact the DOW for
61000-3-2?

Thanks again,

Bob Heller

============================




"cetest" <[email protected]> on 01/18/2000 02:46:52 PM

Please respond to "cetest" <[email protected]>


To:   "Flinders, Randall" <[email protected]>
      "'emc-pstc'" <[email protected]>
cc:    (bcc: Robert E. Heller/US-Corporate/3M/US)
Subject:  RE: Harmonics Testing






I suppose Randy you are concerned about the EN-61000-3-2 instead of the
EN 61000-3-3 which is concerned with Flicker testing.

Please Note that the 3-2 is currently under revision and prone to change
very soon !

I would select Scenario #1

The 50 watt limit is meant to be used for all equipment, and the current
document TC210-169 (in voting right now) has it's clause modified
as such.

Strictly read you are right about the application of scenario #2.

The current 3-2 is a very bad document, f.a. nothing is said about
test times and transitory effects. This will all or partly be covered
in the new version.

BTW Using scenario #2 it will be hard to exceed any limit at all with  an
active input power < 50 watt !!!

Gert Gremmen
ce-test qualified testing


==============================
http://www.cetest.nl
Do you know our
CE/E mark True type Font ?
http://www.cetest.nl/cettf.htm
==============================

>-----Original Message-----
>From: [email protected] [mailto:[email protected]]
>Sent: Tuesday, January 18, 2000 7:12 PM
>To: 'emc-pstc'
>Subject: Harmonics Testing
>
>
>Greetings EMC Professionals!
>
>I have a quick question regarding Harmonics testing to
>EN61000-3-3.  We have an ITE product with a switching power
>supply.  The product uses about 38 watts input power.  According
>to the standard, which scenario applies?
>
>Scenario #1
>
>The unit does not need to be tested, because it falls below the
>Class D Input power range of 75(50)W to 600W.  Section 7.4 of the
>standard states that "...No limits apply for equipment with an
>active input power up to and including 75W...."
>
>Scenario #2
>
>Since the unit does not use more than 75W (or more than 50W for
>that matter), the unit then defaults to the Class A requirements
>and therefor must meet the less stringent Class A limits.  Section
>5 of EN61000-3-3 states: "  Class A: Balanced 3-phase equipment
>AND ALL OTHER EQUIPMENT, except that stated [in Classes B-D]..."
>
>So I guess my question is this: when an ITE product with a
>switching power supply uses less than 50W (75w), does it become an
>exempt Class D Device, or doe sit become a Class A device?
>
>Your insights would be appreciated.....
>
>
>Regards,
>
>
>Randy Flinders
>Chairman
>Orange County Chapter
>IEEE EMC Society
>[email protected]
>(714) 513-8012
>(714) 513-8265 Fax
>
>Note: The opinions expressed herein are personal and in no way
>represent the position of the IEEE, The EMC Society, or my employer.
>

Attachment: winmail.dat
Description: Binary data

Reply via email to