Hi Vito:


>   Could either of you clarify why a double insulated SELV circuit can not be 
> grounded?  Is it a 60950 based or based on some other performance(?) based 
> requirements?

This requires a bit of history.  I don't have all of
the history, but I can fill in some of the blanks.

IEC 536 (1976) is the base document for equipment
classes, i.e., I, II, and III.  Class III required 
the introduction of SELV.

IEC 536 was prepared by the same folks who wrote the
IEC 364 series of standards on building installations.
For these folks, SELV was presumed not to be connected
to ground.  (If they had been in the USA, these folks 
would have considered the doorbell circuit as SELV.)  
The standard did not explicity prohibit SELV from 
being grounded.  The committee was quite shocked to 
learn that equipment manufacturers were using the 
concept for low-voltage secondary circuits and were 
grounding one pole of the SELV.  They did have a 
technical explanation of why grounding SELV was not 
acceptable (which I have forgotten and, at the time, 
I considered faulty).  

In revising IEC 536, the committee then considered the
issue of grounding SELV.  They decided to retain SELV
as ungrounded, and introduced a new concept, PELV
(protected extra-low voltage) which was protected by
virture of being grounded.  They also introduced FELV
(functionally-grounded extra-low voltage).

The IEC 950 folks ignored IEC 536 -- sort of.  They 
did not adopt PELV, but retained SELV.  Instead, they 
did provide for PELV by specifying "Method 3" under 
SELV circuit requirements.  (At one time, several 
European countries did not accept Method 3.)  The IEC 
950 definition of SELV includes a note:  "This 
definition of SELV CIRCUIT differs from the term SELV 
as used in IEC 364."

A SELV circuit can be grounded.  As a result of 
connecting the SELV to ground, the name of the circuit
may change to PELV or FELV, depending on the end-
product standard.  If the end-product standard is
IEC 60960, then the circuit name remains SELV.


Best regards,
Rich







-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Michael Garretson:        [email protected]
     Dave Heald                [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:
    No longer online until our new server is brought online and the old 
messages are imported into the new server.

Reply via email to