I read in !emc-pstc that Rich Nute <ri...@sdd.hp.com> wrote (in
<200111140041.qaa06...@epgc196.sdd.hp.com>) about 'AW: Define Continuous
DC Voltage', on Tue, 13 Nov 2001:
>
>
>
>Hi John:
>
>
>>   SELV can protect under single fault conditions. BUT, as I tried to
>>   explain, under some conditions, it can allow a single fault *to persist
>>   undetected*, until eventually a second, unrelated fault occurs which
>>   then results in a serious hazard.
>
>This is a problem of the double-insulation scheme: one
>cannot know when the first insulation has failed.  So, 
>your argument not only applies to SELV but also to 
>ungrounded accessible metal parts and any other double-
>insulation scheme.
>
>If we pursue your argument, then we should outlaw double
>insulation as an acceptable scheme of protection against
>electric shock, independent of SELV.

No, you are 'extending the argument' until it looks unjustified and then
using that as a hook for your critique. 

I said quite clearly that failure of double or reinforced insulation is
acceptable because failure of it has an acceptably low probability.
>
>And, we should add a "new" criterion that failure of any
>safeguard should be obvious to the operator *without*
>presenting a hazard to the operator.  An interesting 
>design problem.
>
>>   With PELV, this does not happen: the grounding ensures that the
>>   protective device operates. 
>
>This scheme requires that the path between the ungrounded
>PELV pole and the grounded PELV pole be capable of carrying
>the fault current until the protective device operates.  In
>other words, the ungrounded PELV pole must carry 25 amps for
>1 minute (or appropriate criteria). 

Yes, 'appropriate criteria'. 25A for 1 min is an extreme criterion.
Let's go to the other extreme, 150 mA for 100 ms (protection by RCD).

> In turn, this means the
>fault current, 25 amps, must flow from the ungrounded PELV
>pole through the PELV source to the grounded PELV pole.  In 
>my experience, there are few PELV circuits that can meet this 
>criterion.  In the PELV circuits I have worked with, the 25
>A would cause the PELV source to open before the operation
>of a protective device, and the mains voltage would appear on 
>the PELV ungrounded pole.

Yes, because you have deliberately chosen a huge fault current, which is
quite unrealistic in most cases.
>
>>   Well, perhaps I have made it clearer now. My beef with SELV is the ban
>>   on grounding, whereas PELV which is grounded AND double/reinforced
>>   insulated is clearly safer for systems extended in space.
>
>Agreed.  In the products I deal with, this is our construction.
>However, we do not test the capability of the ungrounded PELV
>pole to carry fault current.
>
Well, you might consider *designing* it to carry a realistic fault
current, then there is probably no overwhelming need to test.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Eat mink and be dreary!

-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     majord...@ieee.org
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Michael Garretson:        pstc_ad...@garretson.org
     Dave Heald                davehe...@mediaone.net

For policy questions, send mail to:
     Richard Nute:           ri...@ieee.org
     Jim Bacher:             j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
    No longer online until our new server is brought online and the old 
messages are imported into the new server.

Reply via email to