Michael,

The arcing was between hot and neutral.  GFCI outlets would have made no
difference.

                            - Robert -

       Robert A. Macy, PE    [email protected]
       408 286 3985              fx 408 297 9121
       AJM International Electronics Consultants
       619 North First St,   San Jose, CA  95112

-----Original Message-----
From: [email protected] <[email protected]>
To: [email protected] <[email protected]>
Cc: Robert Macy <[email protected]>
List-Post: [email protected]
Date: Thursday, October 25, 2001 5:52 PM
Subject: 120V Ground Faults


>
>Robert,
>
>>From my experience,  I think you will find that arcing ground faults are
>inherently high-resistance in nature and, while dramatic, do not
>necessarily pull significant amounts of current.  Most 15 amp breakers will
>likely require several seconds/minutes to blow at 60/30 amps, which is what
>you'd get with a 2/4 ohm arc.  In reality, I wouldn't be surprised to see
>something more like a 10-20 ohm figure being used for this type of
>phenomenon, which would allow a 15 amp breaker to arc virtually
>continuously (i.e. the home arc-welder).  The fact that arcs are drawn -
>and sustained - at 120 volts is, I believe, relatively rare.
>
>Higher voltage systems (and GFCI outlets) have ground fault systems that
>rely on the detection of zero sequence (neutral leakage) currents.  My
>understanding is that the decision to require this type of protection on
>480 volt systems over 1200 amps was largely due to the increased likelihood
>they'd be able to draw and sustain an arc, as well as the damage that can
>be caused at these higher power levels (balanced with the concerns of
>cost-effectiveness of installing them more broadly).  I feel they drew the
>line in an appropriate place.
>
>In my experience, while problems, such as this, do arise, the frequency and
>relative damage caused by them is relatively small.  I think you would have
>seen a change (like the addition of GFCI about 25 years ago) if the case
>were otherwise.  You should be able to add zero sequence current sensing to
>your household panel, should you care to do so, for ~$500, but where
>out-of-the-box systems exist for 480 volt systems, this would need to be a
>custom design amploying the combination of a sensor relay and a shunt-trip
>breaker.  Of course any nuisance trips you may experience similar to your
>GFCI would take down your main.... You can buy a LOT of GFCI breakers for
>these dollars.  Caveat Emptor/Engineer.
>
>Regards,
>
>Michael Garretson
>Compliance Engineering Manager
>RadiSys Corporation
>+1 503 615-1227
>
>
>
>                    "Robert Macy"
>                    <[email protected]>         To:     "Dan Kwok"
<[email protected]>, <[email protected]>
>                    Sent by:                      cc:
>                    owner-emc-pstc@majordom       Subject:     Re: skinny
power cords.
>                    o.ieee.org
>
>
>                    10/25/01 02:36 PM
>                    Please respond to
>                    "Robert Macy"
>
>
>
>
>
>
>
>It definitely was not supplied by the heater company.  It was a high
>quality
>UL approved cord.  It's just that this cord carbonized and burst into flame
>as the arc was existing.  The flames did immediately extinguish when the
>arc
>was stopped by unplugging the cord which is good.
>
>But again, it was disturbing that the 15A breaker provided no protection.
>
>Anyway, it was a good lesson for this "sleeping" guy.  Now I take
>electrical
>distribution inside my home much more seriously.
>
>                               - Robert -
>
>       Robert A. Macy, PE    [email protected]
>       408 286 3985              fx 408 297 9121
>       AJM International Electronics Consultants
>       619 North First St,   San Jose, CA  95112
>
>-----Original Message-----
>From: Dan Kwok <[email protected]>
>To: Robert Macy <[email protected]>; [email protected]
><[email protected]>
>Date: Thursday, October 25, 2001 1:42 PM
>Subject: Re: skinny power cords.
>
>
>>
>>Hi Robert,
>>
>>Recently, I bought several similar heaters for my home. I recall reading
>in
>>the operation instructions, explicit safety warnings against using
>extension
>>cords with the heater. Was the extension cord supplied with the heater?
>>
>>
>>---------------------------------------------------------------------
>>Dan Kwok,  P.Eng.
>>Principal Engineer
>>Electromagnetic Compatibility
>>Intetron Consulting,  Inc.
>>Ph  (604) 432-9874
>>E-mail [email protected]
>>Internet  http://www.intetron.com
>>
>>----- Original Message -----
>>From: "Robert Macy" <[email protected]>
>>To: "Roman, Dan" <[email protected]>; <[email protected]>
>>Sent: Thursday, October 25, 2001 8:49 AM
>>Subject: Re: skinny power cords.
>>
>>
>>>
>>> Just have to jump in here with personal experience:
>>>
>>> In our bedroom we have a deLonghi radiator heater which uses an
>extension
>>> cord (high cost UL approved) heavy guage #12 wire to power it - when
>it's
>>> used.  This extension cord plugs into a "multi outlet" adapter, also
>heavy
>>> duty UL approved.  At the time of the incident there was no power being
>>used
>>> from this outlet.
>>>
>>> I was in another room, my wife was sitting on the edge of the bed
>watching
>>a
>>> news blurb on TV when she heard a funny sound, a scritch, scritch.   She
>>> called to me to come listen.  Scritch, scritch, scritch got louder.  As
>I
>>> arrived, flames started lapping up the wall from the outlet while still
>>> making arcing sounds.  The flames were less than 6 inches from curtains.
>I
>>> reached into all this and unplugged the extension cord which luckily
>>stopped
>>> the fireworks display.  Imagine, if we had not been there.
>>>
>>> Upon examination, it appeared that an arc had formed between the blades
>of
>>> the extension cord (remember no power at the time).  That arc was not
>>> sufficient to drop the 15A breaker to the outlet, yet was sufficient to
>>> carbonize the UL approved material which further sustained the arc.
>>>
>>> I posted this to the newsgroup alt.home.repair where a fireman jumped in
>>> describing how this exact mechanism is what starts most home fires!
>Isn't
>>> that an encouraging thought!
>>>
>>> Anyway, a little damn fuse in the plug would not have helped in this
>>> circumstance, complete waste of time, much like the main breaker was.
>>>
>>>                                          - Robert -
>>>
>>>        Robert A. Macy, PE    [email protected]
>>>        408 286 3985              fx 408 297 9121
>>>        AJM International Electronics Consultants
>>>        619 North First St,   San Jose, CA  95112
>>>
>>> -----Original Message-----
>>> From: Roman, Dan <[email protected]>
>>> To: [email protected] <[email protected]>
>>> Date: Thursday, October 25, 2001 7:41 AM
>>> Subject: RE: skinny power cords.
>>>
>>>
>>> >
>>> >I agreed completely with Scott.  A 6 to 9 foot 18AWG cord will handle
>well
>>> >in excess of 20A for a short period of time without starting to smoke
>>> (heck,
>>> >it'll handle close to in excess of 60A for a very very short time
>without
>>> >bursting into flames--not that it was a good experience finding this
>out).
>>> >Point is, the cordage will handle a fault either indefinitely or long
>>> enough
>>> >for the branch circuit breaker to trip provided you are connected to a
>15A
>>> >or 20A branch circuit.
>>> >
>>> >Another data point, you routinely pass more current through the cord
>when
>>> >doing the earthing test and that uses more current than the cord is
>rated.
>>> >Leave the tester on for awhile and the cord does not really heat up
>>either.
>>> >
>>> >What this list needs is a power cord manufacturer or agency safety
>>engineer
>>> >that does power cords to settle this once and for all!
>>> >
>>> >Dan
>>> >
>>> >-----Original Message-----
>>> >From: Scott Lacey [mailto:[email protected]]
>>> >Sent: Wednesday, October 24, 2001 7:43 PM
>>> >To: Gary McInturff
>>> >Cc: [email protected]
>>> >Subject: RE: skinny power cords.
>>> >
>>> >
>>> >
>>> >Gary,
>>> >I believe the answer is that the power cord rating of 6 or 10 amps is
>the
>>> >operating current, at which it will have minimum temperature rise.
>Under
>>> >fault conditions it will experience a rather dramatic temperature rise
>>that
>>> >is still well below the melting temperature of the insulation. The
>breaker
>>> >or fuse should clear well before the cord is "cooked" to the point of
>>> >failure.
>>> >
>>> >Scott Lacey
>>> >
>>>
>



-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Michael Garretson:        [email protected]
     Dave Heald                [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:
    No longer online until our new server is brought online and the old 
messages are imported into the new server.

Reply via email to