Hi David,

You asked/stated:

>Caps to ground can not be greater than .022 uF for FCC impedance
>to ground during ringing limit of 100k ohms, it will still pass FCC leakage
>current test at 6.8 mV @ 1000V.  Have I missed anything about impact of
>caps to ground for European requirements?

Don't forget about the leakage current requirement in clause 6.3.4 of IEC/EN 
60950 2nd Ed. & UL1950
3rd Ed.; and touch current requirement in clause 5.1.8 of IEC/EN/UL 60950 3rd 
Ed. The limit  is
0.25mArms max. in both cases.

Best regards,

Ron Pickard
[email protected]



-------------------------------------------