The following is a guess on my part.  Most household breakers (USA) are 15
Amps for power wires that appliances can plug into.  If a fault occurs, over
the time until the breaker pops, the time averaged current will be somewhat
in excess of 15 Amps.  That means that the time-averaged hazard potential
with a 0.1 Ohm bond will be just over 1.5 Volts, which is not a hazard, even
in a wet area.  I expect that using 25 Amps to test the bond makes sure the
bond path has the ampacity not to fuse open before the circuit protection
device.




----------
>From: [email protected]
>To: [email protected]
>Subject: Bonding Impedance
>Date: Wed, Jul 24, 2002, 3:57 PM
>

>
> Hello all,
>
> I recent issue has come up for me regarding why some safety standards
> specify 100 milliohms as the acceptable impedance for a protective earth
> ground bonding test. I am curious as to what the rationale is for this
> specific value and why 25 amps is chosen as the default test current.
>
> Regards,
> +=================================================================+
> |Ronald R. Wellman                |Voice : 408-345-8229           |
> |Agilent Technologies             |FAX   : 408-553-2412           |
> |5301 Stevens Creek Blvd.,        |E-Mail: [email protected]|
> |Mailstop 54L-BB                  |WWW   : http://www.agilent.com |
> |Santa Clara, California 95052 USA|                               |
> +=================================================================+
>
> -------------------------------------------
> This message is from the IEEE EMC Society Product Safety
> Technical Committee emc-pstc discussion list.
>
> Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
>
> To cancel your subscription, send mail to:
>      [email protected]
> with the single line:
>      unsubscribe emc-pstc
>
> For help, send mail to the list administrators:
>      Ron Pickard:              [email protected]
>      Dave Heald:               [email protected]
>
> For policy questions, send mail to:
>      Richard Nute:           [email protected]
>      Jim Bacher:             [email protected]
>
> All emc-pstc postings are archived and searchable on the web at:
>     http://ieeepstc.mindcruiser.com/
>     Click on "browse" and then "emc-pstc mailing list"
> 

-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:
    http://ieeepstc.mindcruiser.com/
    Click on "browse" and then "emc-pstc mailing list"

Reply via email to