David,

An interesting test, but of course this only characterizes the line at a
single frequency.  It might be useful to check line impedance at other
frequencies as well, say to the 40th harmonic...?   Possibly some modern
line analyzers can do this but it seems to me I once had a working setup
using a control loop analyzer & Bode plotter.  But it has been a very long
time since I look at such things.

Best regards,

-doug

Douglas E. Powell
Compliance Engineer
Advanced Energy Industries, Inc.
Fort Collins, CO 80535 USA



-----Original Message-----
From: Spencer, David H [mailto:[email protected]]
Sent: Wednesday, October 30, 2002 9:57 AM
To: [email protected]
Subject: RE: Measuring AC Line Impedance



Follow up............................

Having just completed an ton of work on this using input I got around here
(thanks to Don Borowski, Patrick Lawler, Joe Randolph and  John Woodgate).
I believe we have characterized the AC mains of our facility.  

As a sanity check/ technical check can any one comment on process.

Part one
1)Open circuit voltage measured.
2)Resistive load placed in circuit.
3) Voltage drop and current measured.
4) Voltage drop divided by current provides  resistance component of AC
mains.

Part 2
1) Open circuit voltage measured.
2)Reactive load placed in circuit (approximately 120uF!)
3) Voltage change (increase really) and current measured (phase angle was
recorded to back check math vectorialy).
4) Voltage change divided by current provides reactive component of AC
mains.


As a side note, I also connected an isolation transformer as the reactive
load,  the reactive numbers were very very close.  

The resistive number + reactive number then make up the AC line impedance
for this site:  Ztest if you will.



My two remaining questions:

Is this method of characterizing the AC line impedance valid (is there
something I'm missing)?

Based on my knowledge of these values, and their ratio to the reference
impedance(s) specified in EN61000-3-3 and EN61000-3-11, I should be able to
calculate and correlate the measured Dmax, Pst, et. al...to the limits
specified in those standards.
(REFERENCE section 6.1.3 of EN61000-3-11), using our existing AC mains.  


Any comments or input would be welcome.
Thanks

Regards
David Spencer
Xerox Corp.


-----Original Message-----
From: John Woodgate [mailto:[email protected]]
Sent: Thursday, September 19, 2002 11:56 AM
To: [email protected]
Subject: Re: Measuring AC Line Impedance



I read in !emc-pstc that Spencer, David H <[email protected]>
wrote (in <052106A55179D611B34300096BB02E3F8B1D@USAMCMS4>) about
'Measuring AC Line Impedance' on Thu, 19 Sep 2002:

>Is anyone familiar with a method to measure and calculate those values.
The
>generic values I have for short circuit condition (which include 4 wires in
>a magnetic conduit) come out higher than my measured values, and those do
>not include the motor generator source.  

Put a large capacitor (mains voltage rated) across the mains and measure
the voltage change; it may actually increase. You need about 50 uF to
get a decent change on 120 V 60 Hz mains. With that result and the one
with the resistive load, you can calculate the source impedance as an R
and L in series.

I'd be interested to learn the result.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk

Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!

-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:
    http://ieeepstc.mindcruiser.com/
    Click on "browse" and then "emc-pstc mailing list"

-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:
    http://ieeepstc.mindcruiser.com/
    Click on "browse" and then "emc-pstc mailing list"

_______________________________________________________________
This message, including any attachments, may contain information
that is confidential and proprietary information of Advanced 
Energy Industries, Inc.  The dissemination, distribution, use 
or copying of this message or any of its attachments is 
strictly prohibited without the express written consent of 
Advanced Energy Industries, Inc.

-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:
    http://ieeepstc.mindcruiser.com/
    Click on "browse" and then "emc-pstc mailing list"

Reply via email to