Richard -

Which edition are you referring to?  2.2.1 in EN60950-1  and
EN60950, 3rd ed., addresses general requirements for SELV
circuits.  In these standards, there is also no
2.9.4.anything.

I'll assume for now that it's 2nd ed., through the 4th
amendment.

2.9.4.2 refers to thin sheet material and accepting thin
sheet material as a valid construction method for Reinforced
Insulation, it must be physically protected; hence internal
to a mechanical enclosure.  This was written into the
standard to allow common transformer constructions to meet
Reinforced insulation requirements and other

2.9.4.1 states Reinforced Insulation can be 0.4 mm, and is
not precluded from being outside the enclosure, *if* it's
not subject to mechanical stresses that can deform the
insulation at normal operating temperatures (it implies it
*can* deform under abnormal operating conditions that lead
to abnormal temperatures).  [Be sure to pay attention to the
Note.]

What you've described seems more like a combination of Basic
Insulation (the inner, single conductor insulation) and
Supplementary Insulation (the jacket).  If the cable is
outside the enclosure, it should be jacketed for mechanical
protection.  Jacketed cables offer many thicknesses of
jacket such that you could readily find one that has a 0.4
mm thickness (16 mils).


Regards,

Peter L. Tarver, PE
Product Safety Manager
Sanmina-SCI Homologation Services
San Jose, CA
[email protected]


> From: [email protected]
>
> Consider the insulation construction for an
> external interconecting cable
> connected to secondary hazardous circuits of ITE
> (EN60950). Is it
> permissible for the reinforced insulation to be
> constructed of two layers
> (e.g., conductor insulation plus external jacket)
> if the total thickness is
> at least 0.4 mm? Clause 2.2.1 appears to allow
> it; however, clause 2.9.4.2
> appears to indicate that layered insulation can
> only be used internally.
>
> Richard Woods
> Sensormatic Electronics
> Tyco International


-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:
    http://ieeepstc.mindcruiser.com/
    Click on "browse" and then "emc-pstc mailing list"

Reply via email to