Peter,

        I am aware of the float voltages and agree that a 60VDC rating
**should be** tested up to 72VDC.  However, I still feel that DC tolerances
are not adequately reflected in the body of the standard.  Is the phrase
"influences of polarity" intended to reference float voltages???

Thx,


Joe

-----Original Message-----
From: Peter L. Tarver [mailto:[email protected]]
Sent: Monday, October 21, 2002 10:30 AM
To: Joe Finlayson; "EMC-PSTC (E-mail)" <
Subject: RE: 48/60 Vdc Centralized Office Equipment



Joe -

When the nominal CO supply voltage is 60Vdc and batteries
are charging, the "float voltage" is closer to 72Vdc.  Test
houses are aware of this and take it into account when
performing their evaluations.


Regards,

Peter L. Tarver, PE
Product Safety Manager
Sanmina-SCI Homologation Services
2000 Ringwood Ave.
San Jose, CA 95131-1749
V: 408-904-2081
F: 408-904-2095
M: 408-234-3529
[email protected]

> -----Original Message-----
> From: Joe Finlayson
>
>       I see section 1.4.5 addressing the
> determination of the most
> unfavorable supply voltage for a test.  The
> tolerance to be taken into
> account is  clear for the determination of AC
> mains powered equipment.  All
> it says for DC powered equipment is that the
> influence of polarity shall be
> taken into account.  I see coming up with  a
> potential of 60VDC either way.
> Was the intent here to state something I am missing?
>
> Thx,
>
>
> Joe


-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:
    http://ieeepstc.mindcruiser.com/
    Click on "browse" and then "emc-pstc mailing list"

-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:
    http://ieeepstc.mindcruiser.com/
    Click on "browse" and then "emc-pstc mailing list"

Reply via email to