David Hello!
 
Open slots or is ok if you have to fixing means (such as bolt and lock
washer) for the connection. This is similar to fork type crimp connectors
which have been acceptable by UL,TUV and other test agencies. 
 
Please note that some test agencies including UL and TUV do not like the
fork type connections if relied upon for earthing and/or earth bonding
connections. You may wish to discuss with these agencies when you use an
open-slot connection for earthing/bonding connections.
 
Best Wishes,
 

This e-mail message may contain privileged or confidential information. If
you are not the intended recipient, you may not disclose, use, disseminate,
distribute, copy or rely upon this message or attachment in any way. If you
received this e-mail message in error, please return by forwarding the
message and its attachments to the sender.




PETER S. MERGUERIAN

Technical Director

I.T.L. (Product Testing) Ltd.

26 Hacharoshet St., POB 211

Or Yehuda 60251, Israel

Tel: + 972-(0)3-5339022  Fax: + 972-(0)3-5339019

Mobile: + 972-(0)54-838175

http://www.itl.co.il <http://www.itl.co.il/> 

http://www.i-spec.com <http://www.i-spec.com/> 



-----Original Message-----
From: David Sproul [mailto:[email protected]]
Sent: Friday, June 21, 2002 11:12 AM
To: EMC-PSTC
Subject: Slotted Busbars


Dear Group,
I have a client who wishes to use open slots instead of closed holes for the
connecting bolts used in joining two 400A busbar within their product.  This
decision was taken to make installation and maintenance easier.  However,
their installation Manager has objected to this without giving a reason.  I
have e-mailed my contacts within TUV and UL, and after some 48 hours they
have not responded.
 
Are there any sufficiently knowledgeable people who can tell me whether or
not this is permissible, and why.
 
Best regards,
David Sproul.