Peter,
 
I do not find your question specific enough: which standards, what fault(s),
where in the world?  Are you considering equipment connected only by domestic
ac mains plugs or also hard-wired or connected using industrial plugs?
 
It is certainly common for product safety standards, such as IEC 60950-1, to
permit the branch protector to protect the power cord in the event of a phase
to earth fault in the equipment, for example.  The need to cater for a variety
of possible time-current characteristics that also vary with rated current is
why we have gone from a simple 1.5 times over-current protector (e.g. fuse or
circuit breaker) rating with no time specified but a maximum of 25A in the
first and second editions to the more complicated test conditions that we have
in the third edition of IEC 60950 and the first edition of IEC 60950-1.
 
Consider also that a building may be protected by fuses or circuit breakers. 
Both fuses and circuit breakers are typically available in a variety of
time-current characteristics.  The fuse standards in the USA are different
>from those used in Europe: ditto for circuit breakers.  At extremely high
overload conditions the mechanical inertia of circuit breakers means that
there is a minimum time below which they will not trip, irrespective of how
high the current goes - this is not true of fuses.  So what fuse or breaker
were you thinking of using to guarantee that a fault in the equipment will
always pull out the building over-current protective device ?
 
Note also that EN 60950-1 has a Common Modification as compared to IEC 60950-1
in this regard (see 2.7.1).
 
Richard Hughes
 


From: peter merguerian [mailto:[email protected]]
Sent: 28 January 2003 19:54
To: [email protected]
Subject: Circuit Breaker Tripping Dring Fault Tests



Dear All,

For safety, it is not clear from the standards whether the main branch circuit
breaker tripping during fault conditions is an acceptable result.

I see no reason why this should not be acceptable. What is your view? Some
third party labs find it acceptable and others do not.

Anyone can lead me to some inernational decisions regarding this issue?

Thanks,

Peter

 

 




  _____  

Do you Yahoo!?
Yahoo! Mail  <http://rd.yahoo.com/mail/mailsig/*http://mailplus.yahoo.com>
Plus - Powerful. Affordable. Sign up  <
ttp://rd.yahoo.com/mail/mailsig/*http://mailplus.yahoo.com> now