I read in !emc-pstc that jules <[email protected]> wrote (in
<2B924D0A9291D511B59300D0B7208EA808DE75@HEMC01>) about 'flicker results
with PWM circuits' on Tue, 18 Feb 2003:

> we have a customer designing and manufacturing  Pulse Width Modulation
>power controllers. These are used in the heating & ventilation industry ,
>within factories and hotels etc. due to the nature of the design switching
>full power on and off between 2 and 30 times a minute it fails flicker
>EN61000-3-3. Looking at the std and doing the maths on a 2kw load, it needs
>to be switching only once a minute to meet flicker requirements. Problem
>with this is only switching once a minute the control is lost !

This is precisely what IEC 61000-3-11 is for, even for products below 16
A. Note that the title doesn't specify 16 A as the lower limit.

The manufacturer has to specify the maximum supply impedance for which
the product meets the flicker requirements, i.e. the limits in IEC
61000-3-3 (including the large Amendment, of course).
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
    http://www.ieeecommunities.org/emc-pstc

Reply via email to