Hi, Richard.

> From: [email protected]
> Sent: Monday, May 12, 2003 5:47 PM
>
> Peter,
>
> I presume that you replying here for product use
> in North America only?

Yes.  UL1310 being a US standard with close ties to NFPA70,
Article 725 and a title of Class 2 Power Units (used to be
titled "Direct Plug-In Transformer Units").  Also, all
standards references were to UL standards, leaving the
distinct impression of a North American only query.
Admittedly, this is sometimes not the case.

> The original question was about meeting LPS
> requirements in UL 60950 and
> Angus McGill asked if having such a supply would
> help in obtaining UL
> approval for the IT equipment (i.e. ITE).

I've already deleted the original posting, but I believe the
question was related to whether or not additional testing of
a Listed Class 2 Power Unit to LPS requirements would aid in
obtaining certification.  If this was the question, the
answer is no.  If the question was intended to go beyond
this, then, certainly, the issues you mention and many
others, still need review.


Regards,

Peter L. Tarver, PE
Product Safety Manager
Sanmina-SCI Homologation Services
San Jose, CA
[email protected]



> From: Peter L. Tarver
> Sent: Monday, May 12, 2003 2:40 PM
>
> Angus & Doug -
>
> Even though 1310 power supplies may only comply with Basic
> Insulation (per UL60950), they have the bejeebers
> tested out
> of them.   UL1310 emphasizes testing over construction,
> whereas UL60950 emphasizes the contrary.
>
> Since a UL1310 power supply must meet the requirements for
> NEC Class 2 power sources, there is no need for any
> additional testing to demonstrate compliance with LPS
> requirements in UL60950.  The LPS requirements are derived
> from (though somewhat less stringent than) NEC Class 2
> requirements.
>
>
> Regards,
>
> Peter L. Tarver, PE
> Product Safety Manager
> Sanmina-SCI Homologation Services
> San Jose, CA
> [email protected]



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
    http://www.ieeecommunities.org/emc-pstc

Reply via email to